Need more info what is the voltage 400?.... and dosn't the same plate express full load current?
 
calculate the current per phase, then set overload to 105%.
 
so, is it single phase or 3 phase?
 
This question will open up a few different views I,m sure but there is no definitive answer. My view is to set overload at between 100% and 110% full load current of motor, if FLC is not on nameplate , work it out from the KW rating
 
single phase. I don't think you can work it form ohms law. its not as simple as that. I seem to remember another equation to work out FLC for motors. I stand to be corrected though.
 
I = P / ( 1.73 * V * p.f)...... for a 3ph motor.

If you dont know your power factor use 0.8 as a all park figure.
We are talking about a 3ph motor here and not single??..... again give all the info you can or we can't head you in the right direction.

Sorry just caught up with last post ....if you drip feed us info then it gets annoying for us give everything you know about the setup pls
 
Apologies. 230v single phase motor as a swimming pool pump. Says 1.1kw on the plate but no FLC or any other KW rating. I need to put a DOL starter on it as whoever installed it before hasn't bothered. The flex feeding it is 1.5 3core and is black! ;-)
 
OK, so flc will be approx. (1100/240) /0.8 i.e. 5.73A, so select an overload 5A -7A, and set at 6A. then clamp it while running to fine tune.
 
you can use 230 if you want, but the actual supply voltage will be closer to 240.
 
If possible clamp the existing set-up beforehand as this formula Tel has used is good for your basic bog standard motor by if you motor is non-standard or specialised then it may have different running characteristics and its to be assumed when clamping that the motor is working within its design parameters i.e. its not overworking due to blockage or bearing wear etc etc...
 
i'd hate to have a blockage or wear on my bearings.
 
If possible clamp the existing set-up beforehand as this formula Tel has used is good for your basic bog standard motor by if you motor is non-standard or specialised then it may have different running characteristics and its to be assumed when clamping that the motor is working within its design parameters i.e. its not overworking due to blockage or bearing wear etc etc...
how would you do this in practice? if the motor was a complete new install I would need to choose the overload before the motor was connected. I couldn't then clamp it until afterwards. chicken and egg type thingy
 