Handed a job this morning;

30kw motor. 55A. Circulation fan on 220°C toaster. Star-Delta setup with thermal overload in at Line contactor. Overload at 40A. D80 mcb tripped. Motor tested and found with negligible IR. Bearings 'lumpy' but felt a lot worse.

So... overload should have been set at 32A... but where was the motor's protection. My two thoughts; 40A at o/l allows 70A at motor or an internal fault.

cabling ok. Contactors ok. Switching ok. Interlocking ok. Need to check overload aux wiring and PLC logic.

ANY THOUGHTS?
 
O/L should be set at 32A if on the load side in delta (you dont say if on supply side or load so assume the normal set-up)

Have you clamped it if possible?
Is their build up on the impeller blades adding weight and extending start up times?
When does the breaker trip if on start-up then exactly when - straight away or on change over?

Any testing to the contactors for internal damage - could be down a phase on contactor load side (drop motor connection off although this may not proof a loaded breakdown of a phase)..

If bearings are lumpy then that alone could be an issue when running full speed
You say a list of OK's but not how you tested and what results... the error here may be how you tested but we won't know without more info.


Be interesting to know if the ELI complies too, a 80A (d) leaves very little room for compliance unless your sitting on the mains and/or using sizable cable.
 
Last edited by a moderator:
what's negligible IR? is that 0.00 Meg or > 999 Meg?
 
what's negligible IR? is that 0.00 Meg or > 999 Meg?

So small. Flat as a Witch's t!t.

Motor had been disconnected before I got the task. MCB tripped during running in delta.

New motor fitted and wired. Belled out from contactors as approx 1.1ohm balanced and an IR of > 999Mohm @ 500V. Voltage between lines at 419V. Start up amps dropped before switchover to delta. Volt drop across contactor in the 20mV region on all six. In the region of 50mV across o/l. Running current at 40A.

Need to check for any restart data prior to failure.
Will check for ELI spec at panel.
 
Motor running at overload by the sound of it... clamp the supply side of Star/delta this should not exceed FLC of plated rating of motor, as it seems the O/L set-up is wrong it seems someone has already been fiddling and trying to overcome nuisance tripping rather than addressing the problem in the first place.

Your post is ambiguous is this a new motor now that has been fitted?... or you reconnected the existing motor.

Is the phase sequence of the contactors supply and load side correct? Incorrect sequence could see many issues like 2 phasing on swap over etc....when you say mcb trips on delta -does it trip at the moment of changeover of after a duration of X amount?
 
Darkwood

Ambiguous? The old motor failed IR test. The new one has been fitted and values from running checks provided.

I'm trying to ascertain why the previous motor died from the info apparent here. Running at 40A line currents is hardly o/load for a 55A motor tho.
 
old things die. it's a fact of life.
 
Darkwood

Ambiguous? The old motor failed IR test. The new one has been fitted and values from running checks provided.

I'm trying to ascertain why the previous motor died from the info apparent here. Running at 40A line currents is hardly o/load for a 55A motor tho.

Where exactly is the overload... star/delta starters can have several options for O/L protection, if its on the output of the main contactor your need to establish if the feed to the delta contactor is taken before the O/L or after this would mean the O/L is set at either 0.58 X flc or the FLC value respectively.

Ive seen most of the methods used for O/L position but normally the supply across to the delta contactor is taken prior to the O/L so this means only 3 of the six motor wires are monitored and you compensate for this by reducing the O/L setting to 0.58 x FLC.

That various O/L positions and tap off for the delta supply have differing pro and cons but most common is on the load side of the main contactor or delta contactor with the delta contactors supply been loops off before the O/L - thus requiring a compensated set-up of 0.58x FLC

If this is your case then the 55amps is reduced to 32amps setting at the O/L - when you clamp 40amps you are clamping the supply lines not any of the 6 motor wires I assume?
 
Last edited by a moderator:
Where exactly is the overload... star/delta starters can have several options for O/L protection, if its on the output of the main contactor your need to establish if the feed to the delta contactor is taken before the O/L or after this would mean the O/L is set at either 0.58 X flc or the FLC value respectively.

Ive seen most of the methods used for O/L position but normally the supply across to the delta contactor is taken prior to the O/L so this means only 3 of the six motor wires are monitored and you compensate for this by reducing the O/L setting to 0.58 x FLC.

That various O/L positions and tap off for the delta supply have differing pro and cons but most common is on the load side of the main contactor or delta contactor with the delta contactors supply been loops off before the O/L - thus requiring a compensated set-up of 0.58x FLC

If this is your case then the 55amps is reduced to 32amps setting at the O/L - when you clamp 40amps you are clamping the supply lines not any of the 6 motor wires I assume?

DW
There is no issue with the set-up. The overload is in the Line supply to afford partial protection in Star and full protection in Delta. I stated in the OP that the overload setting should have been at 32A but found at 40A. The wiring is not the issue. The 40A I measured was on the supply to the 80A mcb what feeds out to the Line and Delta contactors. I had also clamped each line to the new motor when running in Delta... ~17A each. The new motor is not the issue but seems to prove the starter operates adequately.

Things do die... but in Production environments these days, maintenance has been tasked with providing reasons, management want to know how maintenance has allowed said motor to die and then put plans in place to stop everything in their World from dying... that costs and spoils their figures.

Did the overload being set at 40A allow 70A (+ overload factor) at the 55A motor enable the motor to overheat in a high ambient temp (> 40°C) to the point of IR failure?

Did the 'lumpy' bearings cause overload but the protection was inadequate?
 
Sorry to ramble a bit I was just confirming I had read your posts correctly .... and yes yes yes to last post all you suggested could be true but motors go for many reasons and unless it was tested and stripped down its only speculation that can be given.
 
Sorry to ramble a bit I was just confirming I had read your posts correctly .... and yes yes yes to last post all you suggested could be true but motors go for many reasons and unless it was tested and stripped down its only speculation that can be given.

Agreed. Unsure whether the original has been binned.
 
"Lumpy" :stooge_curly: bearings do tend to tighten when the motor is running so could very well have been the problem.
Is the fan hung on the shaft? Vibration from an out of balance fan is a death warrant to the drive end bearing in particular. It takes very little but over time……..

Do you carry out vibration monitoring? We found it very worthwhile on both the motors and the machine. Flagging up a problem before a failure means you can plan the change in an orderly manner. With our wonderful crew it would still be bloody chaos.

Even stood, a motor can suffer from vibration transmitted through the plant. it forms pits in the races where the rollers/balls have been in contact with the same place in the race. BTW it’s called Brinelling.
 