Handed a job this morning;
30kw motor. 55A. Circulation fan on 220°C toaster. Star-Delta setup with thermal overload in at Line contactor. Overload at 40A. D80 mcb tripped. Motor tested and found with negligible IR. Bearings 'lumpy' but felt a lot worse.
So... overload should have been set at 32A... but where was the motor's protection. My two thoughts; 40A at o/l allows 70A at motor or an internal fault.
cabling ok. Contactors ok. Switching ok. Interlocking ok. Need to check overload aux wiring and PLC logic.
ANY THOUGHTS?
30kw motor. 55A. Circulation fan on 220°C toaster. Star-Delta setup with thermal overload in at Line contactor. Overload at 40A. D80 mcb tripped. Motor tested and found with negligible IR. Bearings 'lumpy' but felt a lot worse.
So... overload should have been set at 32A... but where was the motor's protection. My two thoughts; 40A at o/l allows 70A at motor or an internal fault.
cabling ok. Contactors ok. Switching ok. Interlocking ok. Need to check overload aux wiring and PLC logic.
ANY THOUGHTS?