Discuss Motor tripping in the UK Electrical Forum area at ElectriciansForums.net
I agree with Tony, the existing MCB is too small to handle the changeover transient (voltage/current surge) when changing from star to delta. Rather up-size the MCB according to the supply cable and let the overload or manual motor starter protect the motor.
I would have said the 5 second star - delta change over is a wee bit fast , would you not want a figure of more like 10 -15 seconds at least ?
Hi Gents,
i am just trying to get the attachment for a couple of Tonys posts here on motors, but it does not seem that the attachments are working?? or am i just being a dope?
thanks.
Yes this time is a bit tight, I WOULD up this time to around 10s and see how it affects the changeover current, you will do no harm and it takes little time to do. I will probably get shot down, but would think twice before considering to upsize the c/b as the problem was there before the new 63A c/b was fitted and the c/b is primarily to protect the circuit cabling. What size fuses were blowing in old CU ?
Has the motor load increased due to mechanical/process issues recently ?
Oops just seen the age of this post, apologies !! Frosty what was the outcome ?
Reply to Motor tripping in the UK Electrical Forum area at ElectriciansForums.net
BIG place OK lots of electrical bits. but one on a 3 phase Radial is tripping its RCCB so i check the wiring making sure its tight and it has...
Heeelp! I have an 11kW/21A motor which is attached to a hydraulic power pack. I have replaced the old panels with new, using the same star delta...
I have a scenario where there is a three phase DB in a commercial property where there are mixture of three phase and single phase washing...
Hi gentlemen, I have three phase motor has an issue. This motor is star connection. When I just disconnect the power cable coming from MCC...