Also need to consider that the motor should be IE3 compliant, doubt the Chinese have heard of that either!
One other thing to note is the fault level from the converter may be insufficient to operate over current devices in the prescribed time in the event of an over current fault. Maybe worth looking into as this could affect your design and the sizing of your cables.
 