perhaps because it isnt as good a conductor as copper they use the bigger csa size in order to keep earth loop impedance down ??? ( just a though)
no....do you not think the terminal screws wouldn`t get through the tinning?
 
A very good question I thought and to answer it the bare conductor is the same size as the sleaved pvc conductors Biff
 
I've also come across this when doing a eicr, the lighting circuit in the cellar was in 1.5mm fp200 with a tinned copper 1.5mm cpc, the radial sockets however were fed with a 2.5mm fp200 cable with a 2.5mm stranded tinned copper cpc.
 
I’ll say something now.

I’ve never used FP cable or that crazy way of doing 2 way switching and I never will use them. (I’m retired). But I’ve learned several things today, have you?
I very much doubt it!

Members don’t like you’re snide comments, today you have dropped in nearly everyone’s estimation. It wasn’t very good to start with.

Reconsider you’re position and just prey you never have to ask for information.

BTW
I can be downright nasty but if someone asks a question that gets me interested then I’ll help, anyway I can!
 
A very good question I thought and to answer it the bare conductor is the same size as the sleaved pvc conductors Biff

Something else I've learnt today. I thought the CPC was sheathed!

Come to think of it I have re-used early FP. Just don’t ask me where!
A substation I think. Don’t know! It’s lost in the mists of time
 
You do know the easiest way to check (on site that is) would just be grab a coil and your meter and check the resistance of each core on a drum, or see if Line to Earth is same as Line to Neutral............... Just a suggestion if you get any more like this ;)
 
Hmm, Biffs Pis*ed and I don't mean from alcohol, Thats why he is now quiet in this thread and I don't blame him TBH, you start a genuine thread about a genuine issue or question and the prats again are out just like the thread with Glenn, whats happening here, even the good sparks are getting crap now, god help us
 
You do know the easiest way to check (on site that is) would just be grab a coil and your meter and check the resistance of each core on a drum, or see if Line to Earth is same as Line to Neutral............... Just a suggestion if you get any more like this ;)

From experience I know that the size is the same it is just different conductor material,but to test the way you mentioned would not give you any indication of them being thesame or different size,. It will only give a very low Loop L-CPC to compare with L-N, because laminated aluminium tape screen which is bonded to sheath is in constant contact with full size tinned annealed copper circuit protective conductor, so in theory you have 2 CPC’s in parallel if you like.

Al
 
I’ll say something now.

I’ve never used FP cable or that crazy way of doing 2 way switching and I never will use them. (I’m retired). But I’ve learned several things today, have you?
I very much doubt it!

Members don’t like you’re snide comments, today you have dropped in nearly everyone’s estimation. It wasn’t very good to start with.

Reconsider you’re position and just prey you never have to ask for information.

BTW
I can be downright nasty but if someone asks a question that gets me interested then I’ll help, anyway I can!

Just to clarify something, the post I was referring to has been deleted.
I do hope no one took offence by omission.

 
Hmm, Biffs Pis*ed and I don't mean from alcohol, Thats why he is now quiet in this thread and I don't blame him TBH, you start a genuine thread about a genuine issue or question and the prats again are out just like the thread with Glenn, whats happening here, even the good sparks are getting crap now, god help us
let `em come Mike....i`m quite capable of stamping on most of em...
 