paulpinky

Hi All
Looking for a bit of advice if possible. I`m having a new bathroom installed and i`m looking to add an extractor fan, whirlpool bath and underfloor heating. I already have a cable installed into my shower unit which will now be redundant as the new shower will come off the combi boiler. my question is can i now use this supply into a junction box and feed 3 x fused spur links into my new kit. I do have electrical qualifications, but work in industrial not domestic, so I will have to get this inspected by a fully qualified spark. but is the running of the cables to the fuse spur acceptable. Any advice would be greatly appreciated.
 
Depending on loads and size of supply cable (6 or 10mm presumably), wire as a radial from isolation switch. Downgrade protection as required, all to 17th.
 
Thanks for the quick response. Just for clarification my cable is 6mm and is fed from a 32Amp circuit breaker in the CU. could I feed this into an isolator and feed 3 seperate radials from the isolator. also is it acceptable to safely install the isoltar on the outside of the bathroom at high level.
 
If the loads are acceptable, wire the three points as a radial in 2.5 from the isolator. Downgrade to 16 or 20 amp mcb or rcbo as applicable. Full inspection and testing of the circuit will be required, not forgetting part P.
 
thanks for all the advice. i`ll downgrade the mcb as suggested as soon as i get further information with the loadings of the new kit. As for Part P the fan and the underfloor heating will be in zone 3 so they will be fine. just one question about the bath,I think i`m correct in saying that I could put the spur underneath the bath so I would need tools to take the panels off. I have done part p as part of a course but never had to use it so i`m not with a recognised body. but i think i`m correct in saying that i do not have to notify about these changes but will have to get them checked by a fully qualified spark.
 
Not sure i understand about this part P you have done Paul.
Welcome to the site BTW.
 
I did an ugrde to my 16th to a 17th edition in 2008 and got a city and guild qualification for part P. But as I have said I don`t do household stuff so wanted some advice, and if i`m wrong on the notification bit please advise as I do not want to break any laws/guidlines
 
Last edited by a moderator:
Sorry to be picky Paul if you have 17th edt i think you should know about supplies in a bathroom and if C&G have given you luncheon voucher for part P you should also know its all notifiable. I don't doubt your conection skills if you have an electrical qualification but it is simple domestic electrics and from your plan of action it appears a bit DIY in its thinking. sorry fella just my take.
 
fully understand your comments needsasparks but for an industrial electrician it does seem a bit DIY,but without digging out my books and regs i was just after some advice. I was trying to see how much I could do to save on costs etc. probably best i leave it to the proper guys I think. quite easy to pass the exams but more difficult to remember it all if it doesn`t get used. Give me 3 phase motors and invertors any day!!.
by the way i was told by the bathroom fitters that i could do some of the work and they would test it and certify it. I think i`ll put them straight on that too based on all the advice. At least it`s only bang goes the budget and not the cell door lol!!
 
Last edited by a moderator:
its special locations so its notifyable.......its an alteration to an existing circuit so minor works.....check earthing and bonding before undertaking ANY work here and upgrade if necessary.......additional protection by means of RCD will also be required here as well......
 
Sorry Paul, did not read into your OP that someone else was doing the bathroom, so from what you say they will test and register for you so have a word with them if its ok to do what you want to do. Only they can really see what you will end up with and its their name on the job. But it was when you mention putting switched spurs under bath that my ears pricked up. OK if you want it to be a pigs ear, and yes if cables are correctly fused and isolatable and your happy with it, go for it. We don't have to live with it, You do.
You asked our advice and that was mine based on what you said, remember we are only on a PC so we are going to just quote regs to you in relation to your works and if something sounds wrong we will tell you. The important thing is that you are happy with the job at the end and more importantly it is safe. Good luck with your project though.
 