there are instances where sockets do not need to be RCD protected , for instance sockets supplying computors , or freezers it all depends on the designe of the installation cable installation methods etc , as for RCD protection on lighting circuits if the installation is new or you make a modification to a lighting circuit where RCD protection is required then yes and an answer to your question about neusance tripping yes RCD's do trip but not all the time , mcb's can trip too when a lamp goes , so really no real differance between them only that the RCD's are more sensitive due to them detecting inbalance and earth leakages and mcb's are obviously an over load protectinve deice where as an RCD is not , and more often than not if an RCD does trip then its down to a faulty RCD or a fault on the circuit possably an outside light full of water , or mud in the case i had , realistically its the common sense approach thats required , as for the testing side i will give a quick check of the circuits prior to removal of the board just to make sure there are no trapped neutrals in the circuits or low insulation readings , one of the most common problems that you will find and may not show up during the testing is the shared neutral normally on the landing light between the two way switching where the neutral is taken from the first floor lights and the live is from the ground floor lights normally easy to rectify and its easily spotted on a dual RCD board youll find that both RCD's will trip , so in brief look at the usage of the sockets and always do some basic pre tests and the when the board is or being changed carry out dead tests , ring leg to leg the r1r2 Zs RCD tests and i always do a rmap test to hope that helps