gavinrawls

if you was going to install a new cu would you take all the circuits out connect them all up to the new one then test or would you test them before aswell?
 
Gavin - let me start this off by saying you will NOT get a straight answer to this. You will get a load of people telling you to go to college and being a bit sarky with you - the former quite rightfully, the latter quite unhelpful but still rightfully too! The reason is because, if you are trying to do board changes etc, but ask simple questions like this and how to do RCD testing (your other post) then you really REALLY shouldn't be doing this stuff. Sorry to p*** on your parade but this is the case. Electricity is dangerous and needs a fully competent person to work with it.

I'm being gentle with you in saying bite the bullet, go to college, work with someone else for a bit who knows what they're doing - these things should make you competent. In our consumerist, rapid-fire culture we often forget that to learn things it takes time and energy. Short courses are not the way to become a spark. Do a full course mate. I hope you have some joy with it.

I am not against people asking questions. I have asked a lot of questions on here and learnt loads from it. I think asking questions is a very good way to learn but you must have the basics first.

Forgive me if I have made any incorrect assumptions about you.
 
i do know how to go through all the testing procedures beleive it or not but im yet to change a board. I am asking the helpfull experienced electricians if they would test the original board first to make sure the circuits are fine before you open your can of worms and put next one in. for example the ir test. with regards to the rcd testing i found out after i completed my part p assesment that all sockets have to be rcd protected just asking if lights have to be because as you know as an experienced electrician they can be a nuisance. we all have to start some where and id like to get it right from the start and yes i am fully quallified but obviously not as talented as you,.
 
Hello Gavin

...what do you think?

What might happen if you did test everything first? What might you find....?
 
i'll just give gavin the answer now to avoid pages of waffle :-D
before changing CU ;
global ( all circuits at once ) ins res test between L & N to E
measure Ze & Psc at main switch
check bonding / main earthing is in place and of correct conductor size.
quick visual around property checking for damaged fittings.
 
Gavin
found out after i completed my part p assesment that all sockets have to be rcd protected

Do they Gavin ?
Could there be exceptions ?

Forget my post Gavin I see that Spinlondon has already explained it very well for you in your other thread


 
Yep Biff is correct a global IR test a Ze a PSC and a PSSC then check bonding to water and gas. An EICR would be great before any work starts and thats what should happen but in reality no customer will pay for this.

Why well a dead short between L&N to Earth will tell you an RCD will not stay in and that . Ze,PSC,PSSC , tells you that the main incomer is ok and its a good earth.Water and gas gets checked because this needs to be done at the same time.

Thats how I survey a job but I dont give out the readings as I have had a phone call asking I told the other electrician that you did some tests and he would like to see them to compare with his when he does them Aye right
 
The bloke told me at the assessment that any sockets operated by an ordinary person had to be rcd protected I only seen reg to back this up in the osg.im assuming he was wrong.
 
there are instances where sockets do not need to be RCD protected , for instance sockets supplying computors , or freezers it all depends on the designe of the installation cable installation methods etc , as for RCD protection on lighting circuits if the installation is new or you make a modification to a lighting circuit where RCD protection is required then yes and an answer to your question about neusance tripping yes RCD's do trip but not all the time , mcb's can trip too when a lamp goes , so really no real differance between them only that the RCD's are more sensitive due to them detecting inbalance and earth leakages and mcb's are obviously an over load protectinve deice where as an RCD is not , and more often than not if an RCD does trip then its down to a faulty RCD or a fault on the circuit possably an outside light full of water , or mud in the case i had , realistically its the common sense approach thats required , as for the testing side i will give a quick check of the circuits prior to removal of the board just to make sure there are no trapped neutrals in the circuits or low insulation readings , one of the most common problems that you will find and may not show up during the testing is the shared neutral normally on the landing light between the two way switching where the neutral is taken from the first floor lights and the live is from the ground floor lights normally easy to rectify and its easily spotted on a dual RCD board youll find that both RCD's will trip , so in brief look at the usage of the sockets and always do some basic pre tests and the when the board is or being changed carry out dead tests , ring leg to leg the r1r2 Zs RCD tests and i always do a rmap test to hope that helps
 
Flamming heck Nick did you take a breath there?

The bloke on your assessment is almost right.
Socket-outlets that are for use by ordinary persons and intended for general use.
 