Hi all,

Im after some advice please, I have a new chiller to install and want to make sure i have the correct cable size.
The machine has max current use of 152Amps with an inrush current of 292Amps. The cable run is 30 meters long and will be run on perforated tray.
I think i need 50mm2 (3 phase and earth) is this correct?

Many thanks in advance

Kev

P.s im well impressed with this forum, wish i'd found it ages ago!!
 
Well if it's 152amp per phase then 50mm would be fine, by the sounds of things. I'm assuming it's 70c SWA.

You will though in your design have to take power factor correction into account for that size of cable
 
check that current draw, is it 152/292 across the 3 phases, or per phase? if the latter, i would imagine it would be the size of a house!
 