Mentor
Why cant I get the same pliable cable for meter tails that SSE uses the stuff I get is as stiff as rebar whereas theirs is really bendy and easy to form if any one knows why this is let me know
P
 
Pretty sure the meter tails are only single insulated that’s why there so pliable. Where’s as tails are double insulated, quit being soft and grunt through it.
 
No double insulated, I may hijack one of the SSE guys in the roll shop this week and get the low down on this, they have fitted a couple of isolators for me during PME checks which involved changing the cut outs and fitted blue over blue and brown over brown cables
 
with 25mm tails, i pull them up into the CU a few inches extra, strip the ends about 1",then bend ends over when I've got them in a bit of free space. trim ends to get rid of the unequal strands due to bending, then pull down so the ends drop int the main switch terminals. sometimes i even manage to get them thee right way round. :D.
 
The difference is the number of strands. 16, 25 and 35mm insulated and sheathed tails are available in both 7 strand and 19 strand versions. My local wholesaler started stocking the 19 strand a couple of years ago and it is much better to work with than the more solid 7 strand.
 
is the ccc of 19 strand any higher than 7 strand?
 
Manufactures often give a slightly higher current capacity spec for same CSA if the wire is finer strands but it's usually only a few of percent higher. Sometimes finer stranded also has a smaller bend radius allowed, depends on individual manufacturers though.
 