Hi all,

Carrying out a periodic inspection at a domestic installation. Semi- detached house on a row of houses. I cannot for the life of me locate any sign of the earth electrode inspection chamber. Just wondering how you would number this? A 1,2,3 or a 4?

Thanks
 
You need to establish the property has a reliable and safe means of earthing. Can you visually trace the earth? What size is the main earth at CU?

Is Irish EICR coding different to mainland uk?
 
You need to establish the property has a reliable and safe means of earthing. Can you visually trace the earth? What size is the main earth at CU?

Is Irish EICR coding different to mainland uk?
Hi Richy.

Thanks for the reply. I can't trace that cable as it disappears down behind the wall the DB is mounted on.
The main earth coming from suppliers cut out is 10sq.

Yes the coding is different, as we number it 1-4 in terms of the risk involved
 
Hi Richy.

Thanks for the reply. I can't trace that cable as it disappears down behind the wall the DB is mounted on.
The main earth coming from suppliers cut out is 10sq.

Yes the coding is different, as we number it 1-4 in terms of the risk involved
you say there is a main earth from the supply cut-out. does that mean it's been upgraded to PME? what's the Ze?
 
have you tested this unknown earth cable? (earth loop)
Hi James,

No I haven't tested the cable. I'm going to have to return there on Monday. Incidentally, I checked the front of the houses next door and all along that row of houses and there's no sign of an earth rod. Couldn't see any in front or rear of the house I was inspecting either. Very odd
 
Assuming the installation is neutralised, I would give a 2 to an Earth electrode which could not be located as it is impossible to verify that it is correct (or even present). A simple test doesn't prove this.
 

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

YOUR Unread Posts

Daily, weekly or monthly email

Thread starter

Joined
Location
Cork
If you're a qualified, trainee, or retired electrician - Which country is it that your work will be / is / was aimed at?
Ireland
What type of forum member are you?
Practising Electrician (Qualified - Domestic or Commercial etc)

Thread Information

Title
No earth electrode visible?
Prefix
N/A
Forum
Periodic Inspection Reporting & Certification
Start date
Last reply date
Replies
8

Thread Tags

Advert

Thread statistics

Created
An Buachaillín Bán,
Last reply from
An Buachaillín Bán,
Replies
8
Views
1,741

Advert

Back
Top