My gas pipe is definitely straight in the ground, as I can see it - its an ancient iron/steel thing that disappears into the earth. Anyway, I disconnected the bond from the gas pipe and still got 0.46, but then it ocurred to me: as the pipe is connected to appliances which have their metalwork earthed, am I not getting a parallel path through their CPC's? I'm not going to the trouble of disconnecting those, or the bonds on the water pipe or central heating as they are under the floor and a pain in the arse to get to. I'm getting more confused about this by the minute!
The more I think about it I think it is the gas service, as (a) it is a metal pipe going straight into the ground, and (b) the gas-main in the road goes right past the transformer within about 2 metres of it.
Testing the MET without the twig got me 0.35.
i remeber that interceptor thing....could never get into it though...Challenge Ch 125 18:00 weekdays. Brilliant! Interceptor is good too, bit of 80's nostalgia.![]()
May be you can, but if it's iron pipe it will definitely have a wrap below ground (Used to be a grease impregnated tape, which i can't remember the name of at the moment). What you can see, is where it hasn't been properly wrapped after up-stand connection by the original gas fitters. The same will go for the copper pipe, that probably been tee'd of an old main line lead wrapped pipe.
Far more likely that a neighbour or neighbours have had a PME upgrade, and your seeing the results from the bonded services from those properties!!. But you have to remember that your metal service connections, are bonds (as they are in the other properties) and not a recognised earth electrode. So while it is improving your TT system to TN values, it's not really the best place to be!!
Denzo Tape ???
yep...denzo it is...Denzo Tape maybe???
Not sure myself to be honest - it's just a name that's lurking in a dark corner of my mind.
Is that the unbelievably sticky stuff? If so it nearly pulled my hand off once!
Denzo Tape maybe???
Not sure myself to be honest - it's just a name that's lurking in a dark corner of my mind.
Yes, that sounds about right!! lol!! As others say, really horrible stuff to work with, but it works. Must have been around now for 60 odd years or so now, under various names and variations etc!! lol!!
i hope you havn`t been making comparisons Geordie....lol....:biggrinjester:Yes, it's extremely claggy ............ it's like sackcloth soaked in diahorroea and smells like it too.
i hope you havn`t been making comparisons Geordie....lol....:biggrinjester:

Ofcourse, as a temp measure a water main is much more reliable than dodgy reading Ra on an electrode, however it could be replaced with plastic, so any pemenent matalic stucture that is soundly connected to earth and in your opinion doesnt deteriorate is acceptable as a reliable earth in aTT system.
ah...keeping ones nose clean then i see....Not recently Glen.![]()