J
jimjamjimajam
Have been to a customer to fit new hob and oven.
Not only have I now had to rewire half the kitchen but also they're Ze (TT system) is 350+ but they have no bonding to water or gas.
Been in touch with distributor to enquire for PME.
Obvious answer is they need services bonding, but at this rate it's costing them loads.
Any suggestions to overcome this?
Also, customer showed me certs from previous electricians carried out work both showing very different Ze readings. Max demand looks like a guess. And equi bonding is marked down as "advised". Surely that can't be allowed?
Does the gas earth and water need bonding?
How much would it cost for you to install a earth rod or two?
Nope, not really, if the the incoming services are metallic and need main bonding that's what needs doing!! The most important thing is to get this supply PME'd, if it's available on the network distribution supply cable....
Does the premises have an up to date 17th ed RCD CU, or is it still supplied via 3036 fuses etc??
possibly with an upfront VOELCB?..