I understand what everyone is saying here but i give you 2 different scenarios totally then the kitchen ring with a 20a double pole switch connecting a socket for an appliance low level (thats wire theres a switch) years ago when touring some sidn off sites with my old niceic supervisor pointed out to me this was wrong and it needed to be a fused connection as the 20a dp switch was not rated to 32a is this correct I have seen this over the years a few times and noted it as a fault.
also say a 32a mcb then 6mm cable to an isolator 20amp rated iisolator 10amp load air con unit surely doing aan eicr on this the ciruit would need work to repace the isolator? or not potentially something could happen that lets more thn 20amps pull through the isolator surely the isolator has to be higher or equal to the protective device and not just rely on the fact the design current of the load is below the isolators rating or am i missing something
also say a 32a mcb then 6mm cable to an isolator 20amp rated iisolator 10amp load air con unit surely doing aan eicr on this the ciruit would need work to repace the isolator? or not potentially something could happen that lets more thn 20amps pull through the isolator surely the isolator has to be higher or equal to the protective device and not just rely on the fact the design current of the load is below the isolators rating or am i missing something