Calculating the voltage to be able to calculate the full load current of a 850kva 32kv/400v 3 phase transformer with 8% reactance:

400 x 8
100 = 32v

can some one explain this? It won't bloody sink in until I can see why I am 1. Multiplying the voltage by the reactance and 2. Dividing it by 100?? I know it will be simple to you guys...

thanks.
 
yes pls send post the full question or the jon you are working on which is why you need to use this formular. Thanks
 
An 750kva 11kv/400v 3 phase transformer has a reactance of 5%. If a short circuit of negligible impedance occurs on the secondary while rated voltage is applied to the primary calculate the short circuit mva and the short circuit current.

I can remember and calculate the steps but what I am trying to do is understand each step and know why I am doing each step, if you know what I mean.

Thanks.
 
Last edited by a moderator:
1. Find voltage to be able to calculate the full load current

400 x 5
100 = 20v

2. Normal full load current
400
20 = 20

3. Short circuit power
750000 x 20 = 15 mva

4. Short circuit current
15000000
400 = 37.5kva

now I think that's correct but I am having trouble with the particulars of steps 1 & 2.

thanks.
 
You need to calculate the transformers full load current and then divide by the reactance to give the maximum fault current.

This only holds good for a theoretical zero impedance source.
 
Last edited by a moderator:
That should have read 37.5ka (not kva)

thanks for the advice Tony.

So is the answer to step 2 in amps?? Volts divided by volts = amps?? Apologies for being a bit dumb lol.
 
Transformer full load current = (P/3)/(U/√3)
Transformer maximum fault current = FLC/ reactance

I get ((850000/3)/(400/√3))/0.08 = 15.33KA
 
Obvious question on transformer calc, I don't think so! If you want help please get the questions right in the first place.

A thank you would be nice.
 