I have some works at a small flat (4 properties). PME. Service head has been doubled up by DNO, so that supply cable for the second head exits the bottom and feeds the second.

I find a 6mm green/yellow conductor strung between the PME break-outs of the two heads. It looks like the unusual work of a previous installer who didn't know what they were doing. (I have other earthing/bonding to sort to so here that wouldn't be surprising).

But what is odd is both break-outs have DNO seals, which were added after said cable, which implies DNO may have wanted it there (or perhaps they were laughing so much they couldn't be bothered to remove it?)

So WTF is that 6mm cable? Might it be the work of DNO? If so, - why? Note: gas/water bond should (read will..) run only to the MET off the first head. On this basis if the cable were 16mm might it be described as combined bonding/earthing for the RHS suply? - Only the PME in the supply cable between the heads is surely performing that function anyway.

(Please restrain comments on the 10mm tails and 100A fuse.. yes there is work to do here..)

Clicky for full pic..

2 heads.jpg
 
If it ain't broke don't fix it!

I'd be far more concerned about the obvious breach of the gas laws which has been perpetrated by an electrician there, or didn't you notice that bit?
 
If it ain't broke don't fix it!

I'd be far more concerned about the obvious breach of the gas laws which has been perpetrated by an electrician there, or didn't you notice that bit?

Nope.. I was more concerned with working out if there was a MET (Not exactly, but there is a choc-block out of shot where a few other random 6mm green and yellow cables connect together!), why 10mm tails were on that fuse, 6mm Earthing conductors, and if I could fix it without upsetting old people in 4 flats simultaneously (A: No).

What did the gas man do?
 
Nope.. I was more concerned with working out if there was a MET (Not exactly, but there is a choc-block out of shot where a few other random 6mm green and yellow cables connect together!), why 10mm tails were on that fuse, 6mm Earthing conductors, and if I could fix it without upsetting old people in 4 flats simultaneously (A: No).

What did the gas man do?

What actual load is on the 10mm tails? What do they connect to? What size earthing conductor does it require when calculated using the adiabatic equation?

It's not what the gas man did, that pipe is obviously older than the tails, those tails must be at least 50mm away from the gas pipe.
 
I don’t suppose you put a clamp meter on that “earth” jumper did you?

The only time it will cause trouble is if the two feeds are off different transformers or an open CNE. You’ll soon know if either is the case.
 
The fact that there are seals doesn't necessarily mean that the earth cable has anything to do with the DNO. When the meter on the right was changed, the guy may have seen that seals were missing and popped some on everything that should have them.
Just a possibility...
 
Best EV Chargers by Electrical2Go! The official electric vehicle charger supplier.

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

1Justin

Arms
-
Joined
Location
Surrey
If you're a qualified, trainee, or retired electrician - Which country is it that your work will be / is / was aimed at?
United Kingdom
What type of forum member are you?
Practising Electrician (Qualified - Domestic or Commercial etc)
Business Name
Circitas Ltd

Thread Information

Title
odd "earth" cable between 2 PME heads
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
12
Unsolved
--

Advert

Thread statistics

Created
1Justin,
Last reply from
1Justin,
Replies
12
Views
1,439

Advert

Back
Top