Hello, I’ve been asked to rewire an old warehouse and, having had the SWE folk install an isolation switch, I popped in a split CU and have been happily running new cable hither and yon.
However, my C&G Quals were many moons ago and I’ve been fiddling about with telecoms ever since, so my knowledge of wiggly amps is sketchy to say the least (and yes, I do intend to have my work checked by someone registered).
So, if you’ll forgive some numpty questions:
Do the tails to/from the CU need to be crimped?
I’ve been asked to run 10 mm T&E into the CU - the cable won’t fit the punch outs, so can I break out the L/N/E and feed them in separately or do I need to butcher the CU?
Many thanks for any help
 
Line and neutral should pass through the same hole in any situation. You could get a larger stuffing gland for the 10mm2 or come in through containment. Dont forget you need to maintain the IP rating of the enclosure. As for the tails, no they do not need crimping, but need to be correctly rated for the supply and installation method
 
Gents, many thanks for your replies. Even the short one.
Murdoch: it’s split, but it sounds like I’ll have to add another and make it dual.
Cprfenom: you get the prize for the most useful answer.
I have no intention of sitting the Part P and then calling myself a sparkie, but I am trying to make as few mistakes as possible so I have fewer to fix come inspection time. Your helpful advice is much appreciated.
 
Gents, many thanks for your replies. Even the short one.
Murdoch: it’s split, but it sounds like I’ll have to add another and make it dual.
Cprfenom: you get the prize for the most useful answer.
I have no intention of sitting the Part P and then calling myself a sparkie, but I am trying to make as few mistakes as possible so I have fewer to fix come inspection time. Your helpful advice is much appreciated.
Mr Grimm, leave the work to those who know what they are about.
 
Without sounding rude.....it does come across that you may need some help with the design from an electrician who can come and see the job. Do you know an electrician that could come take a look and give you some advice? My initial thoughts are that twin and earth wouldn't be my 1st, 2nd, 3rd etc choice of cable in a warehouse, a split load/dual RCD board would certainly not be my 1st choice of a board in a warehouse. Splitting the cores of the twin and earth and feeding them through seperate holes sounds like a complete bodge and no no if the boards metal. I would seriously consider if your the right person for the job.
 
eddy eddy eddy oi oi oi, T+E for a warehouse? drill a bigger hole in your CU and use tails or SWA depending on where the CU is located and what machinery is going about
CfBh5hVW8AA9-T3.jpg
 
a good choice as a treat would be Laphroaig( spelling might be out).open the bottle smell the peat that it was prepared over. YUMMMEEEEE.

The marmite of malts. Plenty of lovers and haters for that one. I'm a lover though
£25 at ASDA right now too. (I may be researching cheap Malt deals to get a few in for Christmas)
 
Crimped Meter Tails
The meter tails are usually crimped for a good connection, and while I would advise it, it's not actually listed in the regulations (as far as I can see) and therefore not strictly necessary.
However, make sure to check the CU manufactures instructions.

10mm Twin & Earth
I'm intrigued to know what the 10mm twin & earth is being used for? Only in case the cable-calculations are incorrect, no offence though, I'm sure they're fine albeit uncommon. I'd recommend a different CU which can handle the conductor-sizes in question. I wouldn't recommend that you "butcher the CU".

Butchering the CU
Line and neutral should pass through the same hole in any situation. You could get a larger stuffing gland for the 10mm2 or come in through containment. Don't forget you need to maintain the IP rating of the enclosure.
If you meant that the cables can't pass through the same hole in the CU enclosure, I agree with cprfenom. Line and Neutral must pass through the same hole in a conductive (metallic) enclosure to prevent dangerous eddy-currents.
However, many electricians mistake this point in the 3rd amendment to the 17th Edition to mean 'metal CU' when it actually means 'non-combustible CU'. There are non-metallic CUs on the market which are in full-compliance, and there's no need to pass line and neutral conductors through the same hole with these because eddey-currents can't occur.
 
Crimped Meter Tails
The meter tails are usually crimped for a good connection...

I've never seen this. Why would it be necessary? Do you have any example pics?

10mm Twin & Earth
... I'd recommend a different CU which can handle the conductor-sizes in question. I wouldn't recommend that you "butcher the CU".

I'm not aware of any CU that won't accept 10mm² T&E. No need to change it.

There are non-metallic CUs on the market which are in full-compliance...

Do you have any specific examples of non-metallic CUs that comply with Amdt 3 for use in domestic premises?
 
I've never seen this. Why would it be necessary? Do you have any example pics?



I'm not aware of any CU that won't accept 10mm² T&E. No need to change it.



Do you have any specific examples of non-metallic CUs that comply with Amdt 3 for use in domestic premises?
crimping for MCBs and other distribution equipment is mainly for industrial/commercial, although its not a requirement on non domestic it seems to be an unwritten rule.
 

Reply to Old Dog New Tricks ... Renovating an old Warehouse in the The Welcome Forum area at ElectriciansForums.net

Similar Threads

Been looking at a CU change in a small office and would appreciate comments on the following. Office is supplied from the mains intake in the...
Replies
52
Views
6K
Thanks for letting me join the forum! I took my C&G 2360, 2391, 2381 (16th Edition) 15+ years ago, but electrics became peripheral to my...
Replies
6
Views
2K
  • Locked
  • Sticky
Beware a little long. I served an electrical apprenticeship a long time ago, then went back to full time education immediately moving away from...
Replies
55
Views
5K
M
Hi all, I'm new to this forum and just wanted a bit of advise. I have a small NICEIC registered company and usually undertake small to medium...
Replies
4
Views
1K
Hi, I used to post here a fair bit many moons ago but I can't remember my old password not does the password reminder recognise my email so even...
Replies
2
Views
902

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock