yep thats the one they quoted from.

ive no doubt people will not except the NICEIC tech support but as i'm a member i can only follow they guidlines and it does clearly state what they told me in the BPG4

i would be interested to find what nappit etc would suggest as they are supposed to all sing from the same sheet.

any way i am still in full party mood until some one comes up with solid argument against C2 rather than just they personnel judgement

:drummer::clown::party:
 
So if a householder showed you their plug in RCD or RCD protected lead that they always use for outdoor equipment, would you fail their installation anyway as their RCDs don't fall under the scope of your testing and because the NICEIC told you to ?
 
Nope it would get a C2 because the RCD lead is not part of the installation. He could have borrowed it, he could also have another lead that he uses that has no RCD.
Hence change the socket outlet that the lead is plugged into to a RCD protected one and bobs your uncle. Fully compliant, minimum cost and i would do the job there and then for material cost only because you surely wont charge labour for swapping a socket when you are already on site and getting paid for the EICR.

- - - Updated - - -

PS :party:
 
but what's to stop him plugging his lead into another socket that's not RCD protected.?
 
I think you should drop the 'I'm right, told you so party-time' thing - it comes across as quite immature. In my opinion anyway. Daz
 
sorry if the party thing upset you it was purely for the stick i got yesterday.
the regs are full of opinions as i stated in an earlier post but i have also said that this was my opinion from reading the regs and guidelines. others will differ depending on each individual circumstance when doing a EICR.
AS for what happens if he plugs his lead into another socket that argument flows both ways, what if he uses a lead that is not rcd protected.
 
but what's to stop him plugging his lead into another socket that's not RCD protected.?
Naturally assume that customer will always take lead out through same route, perhaps this ought to be written on certificate to cover ones own.
 
Naturally assume that customer will always take lead out through same route, perhaps this ought to be written on certificate to cover ones own.

And you would have explained to them the reason for the socket. You can take horses to water etc.
 
So this then makes a mockery of the whole code c2 then? Talk about doing something for the sake of it! Why not just go the whole hog and change every socket that is within 3m of a door or window, otherwise the next inspecting electrician may follow the Nic advice and change another socket because they found the customer using a different socket to the one you changed! This sort of carry on gives us a bad name.
Eitget solve the problem completely or leave alone.
 
sorry if the party thing upset you it was purely for the stick i got yesterday.
the regs are full of opinions as i stated in an earlier post but i have also said that this was my opinion from reading the regs and guidelines. others will differ depending on each individual circumstance when doing a EICR.
AS for what happens if he plugs his lead into another socket that argument flows both ways, what if he uses a lead that is not rcd protected.

I think what Telectrix was getting at was that if you are going down this route of providing an RCD socket , then why not RCD all of the downstairs sockets ?
Surely if a householder cannot be trusted to use an RCD lead, he can't be trusted to use a dedicated socket ?
 
So this then makes a mockery of the whole code c2 then? Talk about doing something for the sake of it! Why not just go the whole hog and change every socket that is within 3m of a door or window, otherwise the next inspecting electrician may follow the Nic advice and change another socket because they found the customer using a different socket to the one you changed! This sort of carry on gives us a bad name.
Eitget solve the problem completely or leave alone.

The next electrician doing the inspection would only give C3's because there is a RCD socket available.

Think of it as if you were doing a EICR and you can across an external socket outlet with no RCD protection. This is obviously for the use of portable equipment therefore a C2 has to be given. This socket was not installed in the 1940,s so what regulation could you go by except for the current regs.

I hope you understand my trail of thought.

My method of coding is not a money making scheme and i believe we complete the test to prove the safety of the installation. In no way can you give the trade a bad name by following the regulations and guidance notes you just have to explain to the customer your thinking. Is up to them to act upon the report.
 
yep thats the one they quoted from.

Of course they did - they wrote it in the first place!! I take it that you do know the ESC and NICEIC are one and the same company?
 
40 years ago we didnt have electric lawn mowers, presure washers etc but we DO TODAY!! lets move with the times people, other wise we will still be lighting our rooms with coal gas... of which i bet the "gas safe" people of today dont preach well it was ok at the time!!!!!

If theres the potential of a electrical item being used outside the equipotential zone then that person needs protecting and they dont give a sh it if it was safe 40 years ago, they didnt have a electric lawn mower 40 years ago... but they do today... C2 if theres the potential of equipment being used outside.. If upstairs in a block of flats then C3.

Its your name on the cert as miss smith is found laying in the grass holding the cut flex of the lawn mower that she just cut... Cover your arse..
 