K
kosbo
I have to switch all 3 wires - live, neutral and earth too, as it's from 2 different supplies and I do not want to combine earths and/or neutrals, so I need controlled changeover switch or relays...
Or if one or even both customers don't fancy paying their share any more and turn the breaker off.... if one house supply is completely switched off for some reason ( nobody leaves there, went on long holidays and so on) sewage air pump would be still alive (50% time of cause).
If both supplies were permanently live then all you need is a 4 pole contactor with a pair of NO and a pair of NC contacts. Supply the coil of this via a time clock set to switch daily. Just don't switch the earth lol
But who pays for the control supply?
This whole idea of a shared/dual supply is stupid and fraught with danger!
why do you think this is dangerous solution?
Just sit down and think about it!
Are you kidding us?why do you think this is dangerous solution?
Two houses on separate phases, over time the labelling gets misplaced or defaced, guy comes along to work on it, both householders are out, he isolates from the one house he has access to and commences work, midway through timeclock thinks oooo it's time to switch the supply...I am not against of just connecting it to one house and it's simple and easy for me too, but cannot understand what's is wrong with shared/dual supply idea and why it's dangerous...