biff...mr.answer to everything. glenn...electricians forum's most aggressive.

I don't think this is a fair 2 on 1 lads lol.

I agree, i wouldn't code it - i'd repair...obviouslly make the wire off again, but the terminal wants cleaning up. I was just stating what the practice guide IMO said.

...do i get let off now? :)
hmm, now let me see...
i`l think about it...
 
To be fair to all parties, it depends on the purpose of your visit, If the OP is carrying out a EICR, then i think the only course of action would be to code it, if it was me, a corroded terminal due to considerable overheating is a code 1, if the op is there in a working capacity, then cut the tail back, sand and wire wool the metal job done.
 
Cheers High Tower - so we're all right...ner ner
Oohh...hightower...my hero....lol..

images
 
Guaranteed glenn was in tenerife or somewhere and he had his portrait done by 1 of them street guys...and thats the result.
 
Definitely retrievable, but i wouldn't use a file or WD40 or any other oil on the actual contact faces. Get yourself a glass fibre contact cleaning stick. For a bright metal surface without any rough contact surfaces
 