umairde1

Dear All,

Need advice on some strange tripping occurred in our industry, our Protection Relay Micom P111, settings are below,
our relay tripped the VCB on about 75% of overcurrent settings two times and after replacing the protection relay same problem occurred, need support.
Picture attached for reference,

PhaseAmpere
Tripping Values A
259.2​
Tripping Values B
259.2​
Tripping Values C
259.2​
CT Ratio
600​
Setting
0.75​
Setting Ampere
450​
Time 1.5 secs
 

Attachments

  • Image 2023-06-15 at 5.04.30 PM.jpeg
    Image 2023-06-15 at 5.04.30 PM.jpeg
    80.5 KB · Views: 4
Dear All,

Need advice on some strange tripping occurred in our industry, our Protection Relay Micom P111, settings are below,
our relay tripped the VCB on about 75% of overcurrent settings two times and after replacing the protection relay same problem occurred, need support.
Picture attached for reference,

PhaseAmpere
Tripping Values A
259.2​
Tripping Values B
259.2​
Tripping Values C
259.2​
CT Ratio
600​
Setting
0.75​
Setting Ampere
450​
Time 1.5 secs
You need to change your overcurrent protection up to 80% and you should be fine.
 