why? his cabling is in trunking and it's for a light. no requirement to fit RCD protection.

im not 100 percent sure but all sockets must be covered by a 30ma RCD and as your extending the socket circuit you must bring the sockets up to current regs (unless your happy issuing a cirt with "unsatisfactory" on it!!!)
and if i was me i would feel happier putting it on a RCD as its a outside light and the chance of water ingress and also could outside be classed as a special location??
 
if he was fitting an extra socket, then he would need to RCD it. either Rcd the circuit or fit a RCD socket. however, for surface wiring, RCD is not required and neither for an outside light, on the building wall.
 
if he was fitting an extra socket, then he would need to RCD it. either Rcd the circuit or fit a RCD socket. however, for surface wiring, RCD is not required and neither for an outside light, on the building wall.


is a switched fused spur classed as adding to the socket circuit??
 
im not 100 percent sure but all sockets must be covered by a 30ma RCD and as your extending the socket circuit you must bring the sockets up to current regs (unless your happy issuing a cirt with "unsatisfactory" on it!!!)
and if i was me i would feel happier putting it on a RCD as its a outside light and the chance of water ingress and also could outside be classed as a special location??

Unsatisfactory on a MWC ?
icon7.png


Even if he decided needlessly to use an rcd,only the extended part of the circuit would need be rcd protected
 
he meant to check and ensure main bonding to water and gas etc. if that's OK, then i'd charge half a day's labour at your hourly rate + materials.
should i just check bonding is present or should i check Zs at socket before starting job
 
measure Ze first, then Zs at socket. then visually check that main earthing and bonding are there and of adequate size. ( if bonding is 6mm it does not need replacing id there's no signs of damage.)
 
but is it R2 on a bonding conductor? we all call it that, but technically, R2 is the resistance of a cpc.
 
That's getting a little to technical for this time of the week isn't it haha!

What would you rather we called it?
 
If the bonded goes under the floor for a long distance I would do a quick R2 just for piece of mind.

While we are nitpicking, it's "peace of mind" Spinks. As in, your mind is at peace. A piece of your mind is what you give to someone who questions your terminology concerning continuity readings of bonding conductors.
 
call it resistance of the bonding conductor. or perhaps, RbW for water, RbG for gas, RbO for oil, Rbeer for the cellar. :35:
 
While we are nitpicking, it's "peace of mind" Spinks. As in, your mind is at peace. A piece of your mind is what you give to someone who questions your terminology concerning continuity readings of bonding conductors.

Ok I understand