Hi all just
connected up a 3.5KW oven on a 16A 2.5mm radial with 20A DP switch and 1.5mm heat resistance flex .now the oven has turned up,the info has theconnection cable being of heat resisting flex 1.5mm .but on the nextpage states cooker control circuit as being 2.5mm T+e min.
now myway of thinking is cooker control circuit size is the mains supply tothe DP switch. and the flex between the DP switch and oven is the1.5mm flex which is protected by the 16 RCBO.

I Know I have answered my own question but I would like it if some one can secondmy thoughts

cheers

Blue eyes
 
Last edited by a moderator:
Hi all just
connectedup a 3.5KW oven on a 16A 2.5mm radial with 20A DP switch and 1.5mm heatresistance flex .now the oven has turned up,the info has theconnection cable being of heat resisting flex 1.5mm .but on the nextpage states cooker control circuit as being 2.5mm T+e min.
now myway of thinking is cooker control circuit size is the mains supply tothe DP switch. and the flex between the DP switch and oven is the1.5mm flex which is protected by the 16 RCBO.

I Know I haveanswered my own question but I would like it if some one can secondmy thoughts

cheers

Blue eyes

So what are you worried about, you have complied with the manufactures instructions?? Do you think somethings wrong somewhere?? Many of these ovens are manufactured overseas and the instructions translated into English, except that occasionally the translation isn't exactly to the same terminology that we are used too...
 
So what are you worried about, you have complied with the manufactures instructions?? Do you think somethings wrong somewhere?? Many of these ovens are manufactured overseas and the instructions translated into English, except that occasionally the translation isn't exactly to the same terminology that we are used too...

I am not to worried asI was sure i was correct in my install ,I was just after a second opinion of my interoperation of the manual the 1.5mm flex is protected against over current from the RCBO .but the 2.5mm (cooker control circuit) line threw a spanner in the works ,,I wanted to besure I wasn't missing some thing that would get pulled at a latterdate
thanks for your reply
 
Last edited by a moderator:

Reply to oven supply in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi So converting a 6mm cooker connection point into a 13a unswitched fuse spur with the load being a 2.5mm pre wired cable from a oven . is this...
Replies
2
Views
2K
I am replacing my under counter oven with a new 3kw one, oven is on its own circuit and isolation oven switch, the cable is either 4 or 6mm coming...
Replies
7
Views
1K
Need some advice, I have 7 static caravans to connect which need to be connected via TT 1. All the vans have a 30ma RCD main switch internally...
Replies
6
Views
849
I have just had my kitchen redone and the kitchen rewired with a new 6mm cable installed for an electric cooker. However I have changed my mind...
Replies
10
Views
2K
Hi all, I replaced my old Electrolux oven which operated with a 13 amp plug. The new Kenwood oven I ordered says a 16 amp (Requires hardwiring to...
Replies
13
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock