connected up a 3.5KW oven on a 16A 2.5mm radial with 20A DP switch and 1.5mm heat resistance flex .now the oven has turned up,the info has theconnection cable being of heat resisting flex 1.5mm .but on the nextpage states cooker control circuit as being 2.5mm T+e min.
now myway of thinking is cooker control circuit size is the mains supply tothe DP switch. and the flex between the DP switch and oven is the1.5mm flex which is protected by the 16 RCBO.
I Know I have answered my own question but I would like it if some one can secondmy thoughts
cheers
Blue eyes
connected up a 3.5KW oven on a 16A 2.5mm radial with 20A DP switch and 1.5mm heat resistance flex .now the oven has turned up,the info has theconnection cable being of heat resisting flex 1.5mm .but on the nextpage states cooker control circuit as being 2.5mm T+e min.
now myway of thinking is cooker control circuit size is the mains supply tothe DP switch. and the flex between the DP switch and oven is the1.5mm flex which is protected by the 16 RCBO.
I Know I have answered my own question but I would like it if some one can secondmy thoughts