All very interesting but we are supplying general purpose socket outlets not machines with high starting currents (we do not need to use a fusing factor in our calculations), therefore the maximum current carrying capacity of the cable remains at most 36amps; and you are trying to claim that you are protecting that cable from small overloads of a long duration using a circuit breaker that will not operate below 46amps (according to the BS EN time current characteristics graphs that are used as our guidance).
This leaves you with a possible 10amp overloading of the cable during normal use or during fault conditions, which is potentially wasteful and/or dangerous if left unchecked for a period of time!

It would appear that your over complicated approach is no more than another excuse made by people like you after you have simply copied what was there before without noticing the difference between BS & BS EN breakers.
House bashing certainly was very simple before clever people like you started sticking your noses in and embarressing everybody concerned.

I will put it straight and simplified rather than dropping hints...

433.1.1 (iii) states I2 does not exceed 1.45 times Iz ...if this was correct out right your argument would be plausable but....
the following reg' 433.1.2 that in your opening post if your BS EN 60898 meets the requirements of 433.1.1(i) and 433.1.1(ii) this results in compliance with 433.1.1(iii)

simplified - if the rated current of your protective device is not less than the design current & the rated current of your protective device does not exceed the ccc of the cable (calculated) then it is deemed to be in compliance with 433.1.1(iii) relating to I2 not exceeding 1.45 times Iz.

You applied 433.1.1 (iii) to your BS EN devices when they already complied.

Is this easier to understand...
It is also explained simply in appendix 4 section 4.

The over-complicated part was trying to show you that short term and long term small overloads have been factored into these regs and even though you should avoid small overloads for long durations in the design of the circuit (hence the reg exist to tell you this) it wont effect the long term integrity of the cable although its a situation you dont really want, the factors to apply when neccessary and tripping values of devices have so been design to avoid nuisance tripping while not allowing damaging long term overloads.
 
Last edited by a moderator:
So the BS EN 25amp 2.5mm ring and the BS EN 20amp 4.0mm (so called) radial and the BS EN 16amp 2.5mm (so called )radial is the way to go forward.
 
DK - you're over complicating things again, this is why we were given time current characteristics graphs. Simply choose a circuit breaker with an I2 value of less than the CCC of your supply cable and you gaurantee to protect the cable from small overloads of a long duration, we're only talking about general purpose socket outlets here there's no need for rocket science mate.
 
I was showing you why a 20a mcb is acceptable on a 2.5mm cable which contradicts your max 16amp rating if i remember for your radial.
Meeting the requirements as posted above with said device means you automaticlly are in compliance with I2 thus a 16amp can be a 20amp and a 25amp rin can be a 32amp.
 
Look at your graphs johhny - 32amp BS EN breakers do not operate at less han 46amps.
A 4.0mm T&E only carries 36amps, a 2.5mm ring can't carry more than about 42amps and a single piece of 2.5mm only about 27amps.
I can't find my regs book but a 25amp BS EN breaker starts to go at less than 42amps, a 20amp BS EN breaker starts to go at less than 36amps and a 16amp at less than 27amps.
 
and what about the safety factor built in to the CCC values given in BS7671? 27A for 2.5mm cable is BS. it don't even get warm below 40A
 
DK- the basis of your arguement is the use of a fusing factor mate (1.45).
Firstly I'm not using fuses and second I'm not supplying machines with high starting currents, just general purpose socket outlets.

Can you now see why the IET get on my ----.
 
Well I haven't done in 20 years of working in this industry, so I must be doing something right.
 
David, I can see that according to the graph on page 301 BGB that it could be seen as such, but...are not these graphs simplified into simple line graphs from what should realy be much thicker lines?? the standards for BS EN breakers states an I1 value of 1.13In and an I2 value of 1.45In infering that the 32 amp breaker in your example should trip above 1.13x32 =36amps but this could take more than 1 hour.
 