Darkwood
All very interesting but we are supplying general purpose socket outlets not machines with high starting currents (we do not need to use a fusing factor in our calculations), therefore the maximum current carrying capacity of the cable remains at most 36amps; and you are trying to claim that you are protecting that cable from small overloads of a long duration using a circuit breaker that will not operate below 46amps (according to the BS EN time current characteristics graphs that are used as our guidance).
This leaves you with a possible 10amp overloading of the cable during normal use or during fault conditions, which is potentially wasteful and/or dangerous if left unchecked for a period of time!
It would appear that your over complicated approach is no more than another excuse made by people like you after you have simply copied what was there before without noticing the difference between BS & BS EN breakers.
House bashing certainly was very simple before clever people like you started sticking your noses in and embarressing everybody concerned.
I will put it straight and simplified rather than dropping hints...
433.1.1 (iii) states I2 does not exceed 1.45 times Iz ...if this was correct out right your argument would be plausable but....
the following reg' 433.1.2 that in your opening post if your BS EN 60898 meets the requirements of 433.1.1(i) and 433.1.1(ii) this results in compliance with 433.1.1(iii)
simplified - if the rated current of your protective device is not less than the design current & the rated current of your protective device does not exceed the ccc of the cable (calculated) then it is deemed to be in compliance with 433.1.1(iii) relating to I2 not exceeding 1.45 times Iz.
You applied 433.1.1 (iii) to your BS EN devices when they already complied.
Is this easier to understand...
It is also explained simply in appendix 4 section 4.
The over-complicated part was trying to show you that short term and long term small overloads have been factored into these regs and even though you should avoid small overloads for long durations in the design of the circuit (hence the reg exist to tell you this) it wont effect the long term integrity of the cable although its a situation you dont really want, the factors to apply when neccessary and tripping values of devices have so been design to avoid nuisance tripping while not allowing damaging long term overloads.