I don't have my regs book to,hand right now, but what about the reasonings I gave rather than just a politicians answer to a question.
 
Well you have not answered my first question about the IET, or do you just pick and choose what to answer?

oh and you are not my dad so please don't call me son, thank you.
 
I spoke at length to the IET on this subject as it happens, they couldn't come up with an answer.

But did react by removing the time current characteristics graphs from the 17th Edition (to try to hide their error)!
 
Why is it? You choose to on here and educate people but can't back your
thoughts up with any evidence that proves it.

Exactly waht 'evidence' are you looking for?
Can you not read time current characteristics graphs.
 
And how much energy has been wasted because you haven't found faulty appliances?

How long are your installations lasting before the cabling becomes damaged and unusable?

I believe there has been a increase in electrcal fires and exploding gas mains, so stop trying to wind me up, you've got nothing useful to say 'son'!
 
I think you need to read the rules and show a little respect round here, people have opinions and will express them freely without ever resorting to name calling. I have never called you names just questioned your logic and thinking, if you don't like that the maybe you should not post the on a public forum.
 
You've yet to say anything constructive that I've noticed my friend - you're just on the wind up.
 
Am I? I have questioned and quieted your reasoning yet you struggle to answer properly my questions, give me a answer with reasons that can be backed up with proof thenI will happily say yes,you are correct.
 
I'm intrigued, but not quite grasping what your saying......are we not talking about overload here and the thermal strip in the breaker?? so as I see it the standards say that this will not trip below I1 which is 1.13In, but it will trip above this and within 1 hour at 1.45In.......



32amp BS EN60898 I1 = 36amps (>1hour) I2 = 46amps (1 hour)

32amp BS 3871 I1 =32amps (2hours) I2 = 43amps (1hour)


Therefore as the current creeps above 36 amps the strip heats and after time it will eventually trip, but will take longer than 1hour?
As the current creeps above 46amps the strip will reach a temperature causing the breaker to trip in 1hour?

How long can the cable insulation withstand these smaller overloads (4mm 70 deg T&E Ref C @ 37amps) well I suppose until it reaches above 70 deg and the insulation begins to degrade, but to be honest I dont have a clue as to how long that would take.....but I'm almost certain that by following the formula Ib<In<Iz and as such I2<1.45Iz then the cable will have been selected to satisfy protection for small overloads for long durations....
 