Hi everyone new to the site.
I have read other threads on this but still a bit unsure. I have been asked to wire a supply to a mates garage and i am just looking for a couple of pointers.
I havent done this type of instal before so excuse my ignorace if i have a couple of things wrong.

I plan on wiring overhead on a caternery wire as underground is not an option.
Supply will be in 6mm SWA 3core using a core as earth, the run will be 25m MAX, there is no extreneous metal or service pipes in the garage.
I will be coming off a 32a mcb in the house DB which is RCD protected and going to a metal clad CU with a 16a and a 6a mcb to power a double socket which will supply a freezer and occasionally a lawnmore. The 6a will be for a flourescent light fitting. I am quite happy that this is ok. If not please feel free to correct anything.

The problem i am having is the garage itsself is only 2.5m high and my mate doesnt really want a pole coming up from his garage to meet the 3.5m height requirement altho the point i exit the house is just over 3m.

The distance from the where i plan to exit the house to the point i enter the garage is 3-4meters. And doesnt cross a driveway it will cross a small path and over bushes until the garage.

Will i have to insist on bringing the hight up or will it be ok crossing the path at a slight angle down to the garage?


Thanks
 
lift the garage end to 3m to match the house end. over a path, should not cause a problem.
 
As above. Also make it strong enought that if/when the window cleaner hits it with his ladder the thing doesn't break.
 
The regs are a guide - so discuss the options with the client, confirm the agreement in your quote/estimate and again on your invoice.
 
Thanks. I did think the 3.5m was a guide and ultimatley its common sense.
The hight the cable will be at above the path will a shade under 3m then its over hedges and bushes. My mate is happy with that so i'll go for that. Thanks for the advice
 
Just a thought. Unless your mate is going to be wealding hegde trimmers about why not use hi tuff cable. A lot lighter than SWA. It seems like a long run to be suspending that sort of weight.
 
Just a thought. Unless your mate is going to be wealding hegde trimmers about why not use hi tuff cable. A lot lighter than SWA. It seems like a long run to be suspending that sort of weight.

Hi tuff usually costs more than SWA due to it not being a standard stock line for most wholesalers. H07-RNF flex would be a better choice IMO.

4metres is a short run!
 