Just one on each board each CCT is supplied by mcb
Just 1 on each board the circuits are just fed by mcb'sAhhhh, how many rcds you got?
With using rcbos for each circuit does this mean then that each circuit will have 30mA as opposed to every circuit having 30mA off the main RCD?Items with switch mode power supplies such as laptops, PC's, printers etc can have standing leakage up to 3mA per device and this wouldn't be considered a fault current. From the load you describe there could be standing leakage in excess of 20mA which doesn't leave much before the 30mA tripping threshold is reached. Maybe clamp the live and neutral together in an earth leakage clamp meter and measure the normal standing leakage with all appliances switched on. You may need to install RCBO's on each circuit rather than a single main RCD.