Hi Guys I hve a ring main that keeps tripping, but it also trips the main rcd on the board, is there a possibility that it is being overloaded? There are about 6 computers a franking machine a photocopier coffee machine and a few other gadgets on this one ring of 10 sockets! Should the ring be split down to maybe 2 or 3 seperate rings??? Take into account this is on a second dist board in a house that has had a conversion for a small office. There were only 3 lights and 10 sockets added on.
 
sounds more like a leakage problem. do the usual tests. IR being the favorite.
 
The circuit runs for a few days and then just trips the breaker and kills the whole board
 
There are about 6 computers a franking machine a photocopier coffee machine and a few other gadgets on this one ring

Items with switch mode power supplies such as laptops, PC's, printers etc can have standing leakage up to 3mA per device and this wouldn't be considered a fault current. From the load you describe there could be standing leakage in excess of 20mA which doesn't leave much before the 30mA tripping threshold is reached. Maybe clamp the live and neutral together in an earth leakage clamp meter and measure the normal standing leakage with all appliances switched on. You may need to install RCBO's on each circuit rather than a single main RCD.
 
  • Like
Reactions: 1 person
could be the computers as cheap psu's can leak power to earth as they are always drawing power even when not powered up
 
Items with switch mode power supplies such as laptops, PC's, printers etc can have standing leakage up to 3mA per device and this wouldn't be considered a fault current. From the load you describe there could be standing leakage in excess of 20mA which doesn't leave much before the 30mA tripping threshold is reached. Maybe clamp the live and neutral together in an earth leakage clamp meter and measure the normal standing leakage with all appliances switched on. You may need to install RCBO's on each circuit rather than a single main RCD.
With using rcbos for each circuit does this mean then that each circuit will have 30mA as opposed to every circuit having 30mA off the main RCD?
 

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
overload
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
21

Advert

Thread statistics

Created
Norn Iron,
Last reply from
sp4rk13,
Replies
21
Views
2,701

Advert