I discovered while visiting an elderly neighbour she was using a 2 socket 2m long extension lead wired with 1mm2 PVC 3 core (- both a Duraplug double socket and 13 amp and 10 amp fused plug) to supply her ironing board in her lean to extension on which she had plugged a 2.2kW steam press and 2.4kW steam iron. She had been using this arrangement for a year. No visible (internal or external) problems to any of the electrical components. Extension supplied and wired by a friend who was a retired electrician. Even a label near plug to only fit a 10 amp fuse. Extension originally used for lady's sewing machine and a lamp but then change of use for the ironing and pressing arrangement now.

Thoughts invited on whether to continue with this arrangement.
 
Are you sure the extension lead is 1mm and not 1.5 which is more common?

If the leads aren't getting warm to the touch during use then I'd say they're fine. Are they supplied by a circuit with RCD and MCB protection innthe CU? You could always test at the end of the lead and calculate the disconnection time in the case of a fault.
 
Those power ratings only apply while the elements are on. As both the press and iron will be thermostatically controlled, their loading will cycle between 2.2/2.4 kW and zero so there is a bit of diversity. An iron on medium setting might only be on half the time, in which case the average heating of the cable will be halved (although not quartered as it would be with an element of half the power switched on all the time). As the thermal time constant of the cable is probably similar to that of the iron, it probably doesn't exceed its rated temperature despite the theoretical possibility of overload.


That said, I hate undersized extension cables. 1.25 minimum, preferably 1.5 for a 13A. Why bother with anything less?
 
Last edited:
Those power ratings only apply while the elements are on. As both the press and iron will be thermostatically controlled, their loading will cycle between 2.2/2.4 kW and zero so there is a bit of diversity. An iron on medium setting might only be on half the time, in which case the average heating of the cable will be halved (although not quartered as it would be with an element of half the power switched on all the time). As the thermal time constant of the cable is probably similar to that of the iron, it probably doesn't exceed its rated temperature despite the theoretical possibility of overload.


That said, I hate undersized extension cables. 1.25 minimum, preferably 1.5 for a 13A. Why bother with anything less?

Thank you to you all for your replies. As it plays on my mind I will do the right thing and replace his arrangement for her press and iron. I like margins in cables - it is IsquaredR after all that produces the ohmic heating in them. I will buy some 1.5mm2 and provide two single socket extensions one for the press and one for the iron and band them together for neatness between her ironing board and the double socket she uses. I will look at her consumer unit at the same time. I suspect it is a fusebox. Some work hopefully in the offing for a local sparks I know who will do a good job at a good price and the necessary inspection and testing (and any required remedials).

As well as making good tea and cake she is a real character to talk with.
 
Good luck with trying to get 1.5mm² into a duraplug! It'll be a real struggle for sure! As it wont only be tea and biscuits you'll be having, you'll still be there at tea-time also! I would use either 1.25mm² in your setup or 1.5mm² in an MK 'toughplug'.
 
Last edited:
Good luck with trying to get 1.5mm² into a duraplug! It'll be a real struggle for sure! As it wont only be tea and biscuits you'll be having, you'll still be there at tea-time also! I would use either 1.25mm² in your setup or 1.5mm² in an MK 'toughplug'.

Duraplug 13A plugs are designed to accept up to 2.5
 
Really! Definitely not the ones I've come across which you'd struggle to get 1.5's in. Have you a part number or link to these please.

I take it back, I was wrong. Either my memory is failing or the spec has changed but the Duraplug 13A and 15A are only specced for 1.5
The older ones could take 2.5, unless it's the permaplug I'm thinking of. We get through so many of the damned things I think I fit them half asleep now anyway.
 
I take it back, I was wrong. Either my memory is failing or the spec has changed but the Duraplug 13A and 15A are only specced for 1.5
The older ones could take 2.5, unless it's the permaplug I'm thinking of. We get through so many of the damned things I think I fit them half asleep now anyway.
We only use these now: Tough Plugs the 'pvc top' ones and in my opinion they are the best plug-tops on the market!
 
Last edited:
Although the 13A Duraplug is designed for 1.5 and it fits nicely, they will take 2.5. It's tight but the result is sound if you are careful. We went over to Permaplug for our 15A but then started having quality control issues, mainly bad terminal screw threads, so returned to Duraplug.
 
Although the 13A Duraplug is designed for 1.5 and it fits nicely, they will take 2.5. It's tight but the result is sound if you are careful. We went over to Permaplug for our 15A but then started having quality control issues, mainly bad terminal screw threads, so returned to Duraplug.

I hate 15A permaplug, they're all plasticky and horrible, almost as bad as Walther commando plugs :( Duraplug is much better.
 

Reply to Overloaded extension cable or not? in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Some advise or views would be appreciated. My supply is 100 amp single phase. I purchased my property 3 years ago or so, the owner prior to the...
Replies
29
Views
789
Strange on this, we are wiring an extension at the moment and I would like to 3 way the (currently 2 way) landing switch to the new bedroom so...
Replies
14
Views
586
I am looking for advice on getting an upgraded 25 meter extension cable from my office into my car park to charge my EV from an IP66 rated socket...
Replies
7
Views
1K
Here's a Sunday puzzler for you all..... I've a large rental stock of properly made up mains adaptors for use in Europe and elsewhere - so...
Replies
9
Views
1K
Hi all. Have an issue i'd love some advice on if anyone would be so kind. Will try to be brief. Thank you!! So, have an intermittent RCD trip at...
Replies
43
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock