Circuit Design, Power Systems and Electronics Related
Hello

Looking at a job in an old building where the mains enters the building straight into a busbar chamber.

The building has 3 floors with a distribution board needed on each floor.

Would a panel board be required here, with say a 400A main switch and multiple outgoing 100A devices?

Or would it be acceptable to supply 3 x 100A TPN fused switches from the busbar and do away with the 400A panel?

Not really sure what the panel would achieve here other than being capable of shutting down the full installation, but this could alternatively be done by turning off the 3 x fused switches.

Thankyou
 
A single point of isolation would be far better.
My preference would be for a panel board.
Although you could achieve the same with isolators and the bus bar chamber.
 