I should clarify regarding the lifting of tiles that the margins I suggest are for the edges of the panels to the margins of the roof. Assuming you are using panel base rails, your hooks can be upto 500mm from the edges of the panels (so 1m away from the roof edge for a concrete interlocking roof) with no chance of damaging the verge cloaking detail.
Bear in mind that if you are going into the roof edge zones you really want to keep the panel / hook overhangs to less than 300mm ideally. It depends on the rail / hooks you are using, the rafters details and expected windloads.
Another thing, when I worked at SC (back at the start of the century) we did some testing at BRE which suggested that with some rail / panel combinations oscillation could occur which would gradually loosen mortared ridge tiles.
Another reason to keep panel overhangs as short as possible...