hello all
been a while just wanted to check a couple of my calculations for part F have a background ventilator (trickle vent ) marked up 2500mm EA, is the figure used for the table in Part F the way i have used it before is this way as it marked on the back of the unit. am i correct?
any help would be appreciated
 
I cannot quite make out to which table you are referring or how it relates to the trickle ventilator.

However the 2500mm² EA on the vent is the equivalent are of the vent and can be used as part of the background ventilation required for rooms, it is the minimum area for wet rooms and half the minimum area for habitable rooms.
 
I cannot quite make out to which table you are referring or how it relates to the trickle ventilator.

However the 2500mm² EA on the vent is the equivalent are of the vent and can be used as part of the background ventilation required for rooms, it is the minimum area for wet rooms and half the minimum area for habitable rooms.

Hello Richard Burns
Part F document page 23, System 1, states for a 1 Bedroom Flat/House Equal to or less that 50m2 =25000mm2 EA for a leaky house/flat or airtight is more.
 
So for a one bedroom flat above the fourth storey you need a total of 25,000 mm² equivalent area of background ventilation.
For a one bedroom house on its own then you add 10,000 mm² so need a total of 35,000 mm² equivalent area of background ventilation.

Each habitable room needs minimum 5,000 mm² EA, each wet room needs minimum 2,500 mm² EA.

The ventilator you mention would be suitable for a wet room or you could use two in a habitable room to meet the minimum requirements for the room.
However suppose the 1 bedroom house had a living room, kitchen, bedroom, toilet and bathroom. The total minimum for each room would be 5,000 + 2,500 + 5,000 + 2,500 + 2,500 = 17,500 mm² EA so you would still need to add another 17,500 mm² to make it up to the whole house minimum of 35,000 mm² EA.
 
hello Richard
yes page 22 also has the way it is calculated also & now uses EA for the whole flat or house even if not on the 4th floor.
doing a lot of these certificates.
 

Reply to Part F background ventilation problem in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hello, I understand that from the 15th of June testing and commissioning of vents and fans is now compulsory and that also since last year any...
Replies
47
Views
4K
I have pulled out an old evaporative system I purchased many years ago from storage to have a look at it and see if I can get it running. Was...
Replies
1
Views
191
Evening all, I had a quick Friday afternoon domestic job that has turned into a PITA and I'd appreciate your help. While adding some new lights...
Replies
10
Views
838
Hi I have a 3phase shop in a high humidity area in (Hawaii) and I'm having some issues with low voltage on the single phase outlets on the 120v...
Replies
6
Views
873
HI There, I would be grateful if you could help me, I have a very long duct between the bathroom and extractor outlet vent and for sometime, the...
Replies
3
Views
991

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock