Hi everyone, I hope that you can offer some assistance on this one for me.
I have just viewed some apartments with underground parking where the lighting is constantly on . The lighting is provided by 12 x 70W flourescent lamp units. On each of the 3 entry points the original electrical contractors have fitted Robus PIR units. These PIRs state tht they are capable of carrying 300W - not the 840W (not to mention the 1.8 x start up calculation) required. Two units appear to be stuck in the on position and one appears to be stuck in the off position.
I can't find a PIR that is capable of switching this level of current so will I have to use a contactor and if so (since I've never fitted one before) how would I go about incorporating one in to a trunking system?
Apologies if that sounds like a stoopid question and any pointers as to a specific product would be much appreciated.


Cheers
Chris.
 
You would install the contactor near the db or circuit origin and connect the pir and lights to it.
 