Discuss Please help my head is fried from open earths in the Electrical Forum area at ElectriciansForums.net

Welcome to ElectriciansForums.net - The American Electrical Advice Forum
Head straight to the main forums to chat by click here:  American Electrical Advice Forum

Thanks in advance.
Carried out test on a socket circuit today and found open circuit on cpc’s and lives. Sorted out lives, but earths are driving me crazy. I’ve done all the obvious like connected one earth and then testing sockets etc etc.
In the end after disconnecting everything from earth bar( including main earth, all bonds and all cpc’s ) I was still getting a loop reading at all sockets. Max Zs reading taken was 1.26 ohms).
I can’t for the life of me find out where the sockets are getting a near perfect earth from.
Any info or ideas would be greatly appreciated.
 
Wetroom Store - Network Wetroom Suppliers
This official sponsor may provide discounts for members
Advertisement - Content continues below

Andy5678

-
Arms
Esteemed
Thanks in advance.
Carried out test on a socket circuit today and found open circuit on cpc’s and lives. Sorted out lives, but earths are driving me crazy. I’ve done all the obvious like connected one earth and then testing sockets etc etc.
In the end after disconnecting everything from earth bar( including main earth, all bonds and all cpc’s ) I was still getting a loop reading at all sockets. Max Zs reading taken was 1.26 ohms).
I can’t for the life of me find out where the sockets are getting a near perfect earth from.
Any info or ideas would be greatly appreciated.
Are you testing ring continuity? What are you results? Why did you decide to disconnect everything from earth bar? What is the circuit wired in? I have so many more questions on your testing methods as they seem a bit random
 

ashrow

-
Arms
I have found open cpc's where some one has drilled direct center of the twin and earth, put a rawl plug in and there you go.
Good luck in finding the break.
Have you donre a insulation resistance test ?
Are the sockets RCD protected as it may be a neutral to earth fault helping those reading
 

Megawatt

-
Arms
Advent Win
Thanks in advance.
Carried out test on a socket circuit today and found open circuit on cpc’s and lives. Sorted out lives, but earths are driving me crazy. I’ve done all the obvious like connected one earth and then testing sockets etc etc.
In the end after disconnecting everything from earth bar( including main earth, all bonds and all cpc’s ) I was still getting a loop reading at all sockets. Max Zs reading taken was 1.26 ohms).
I can’t for the life of me find out where the sockets are getting a near perfect earth from.
Any info or ideas would be greatly appreciated.
Dlt21 first off a very good earth is a good thing but you say you have every earth took loose on doth ends. What about the earth under the floors, gas line, water lines etc.
 
  • Thread Starter Thread Starter
  • #7
Carried out insulation resistance test and got 10M ohm. L and N’s = 0.54 ohms end to end. Protected by 61009 RCBO. Checked polarity etc. Plastic incoming water and copper gas
( disconnected at earth bar)
What I’m confused about is why I’m getting such a good earth and where it’s coming from. It’s a TNS with a supply in and supply out
( presume to next property) from cut out. Thanks again
 
  • Thread Starter Thread Starter
  • #9
2.5mm T+E. I took a video, but too large to upload unfortunately. Boiler is wired off socket circuit, but like I said main bonds disconnected from earth bar. Was wondering if getting reading because parallel earth through sockets cpc’s joined to gas pipe via boiler spur and through gas pipe to neighbours gas pipe and back through his earth..if that makes any sense.
Thanks
 

Baddegg

-
Arms
Supporter
Esteemed
Advent Win
How old is the property, I’ve had an old one in the past where someone had banged a random earth rod into the bare earth under the floor and run a fly lead from the back of a socket! No idea why and only found by chance when looking for a faulty cable....
 
  • Thread Starter Thread Starter
  • #14
It’s an old brick built building.. I was thinking sockets might be connected to earth rod somehow, but wouldn’t expect such a low reading of earth rod....
Post automatically merged:

Disconnected everything from sockets when tested.
 

Andy5678

-
Arms
Esteemed
temporary rewire sections between sockets (on the outside of the walls) leaving existing disconnected, until you get continuity and then narrow down the break. You could use a long lead and just go between CPCs
 
uHeat Banner - Forum Discount Available
This official sponsor may provide discounts for members
Advertisement - Content continues below

Reply to Please help my head is fried from open earths in the Electrical Forum area at ElectriciansForums.net

uHeat Banner - Forum Discount Available
This official sponsor may provide discounts for members
Advertisement - Content continues below
Advertisement - Content continues below

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
Advertisement - Content continues below
Top Bottom