Leave one of the cpcs connected to the earth bar and retest ring continuity to the disconnected one, if you have continuity you have a parallel path. I assume IR tests are clear.
 
Connect one cpc to its live at the board, test for continuity at each socket. Check in the last socket that gives continuity (if unclear how it is wired, check those that have highest continuity reading). If necessary, repeat with the other leg at the board. If no loose connections, it may be faulty between the 2 sockets identified.
Don't worry about the mysteriously good Zs with no cpc connected. It's not as important as the non-continuous cpc.
 