The MI3000 needs to be on LOOP, and carry out on incoming side of main switch with main earth disconnected.

The MI3000 can not perform a fall of potential but if supply is present then it is capable of testing Ra via Loop setting.
 
no, he needs an Ra, all rods need an Ra test doing,
but as he is obviously not that bothered, like a lot of 'electricians' out there at the minute he will settle for a Ze cos he doesnt have the test kit [or possibly knowledge] to do an Ra
heck, due to all the Electrical Trainee they have even changed the onsite guide to allow for Ze if an Ra isnt available, its a mockery, and then people moan about why gasmen get decent money when we have 5week wonders running amok,!!!

OK, you're obviously an experienced sparks. For the benefit of the less knowledgeable amongst us, can you please outline the relationship between Ra and Ze and explain why it's so important to get an Ra measurement when the critical value for the disconnection time of OCPDs is Zs (and therefore Ze).
 
Please correct me if I'm wrong or miss out anything important to this......


RA is the reading of the resistance within in the ground conditions of the earth electrode only. Tests are carried out without the main earth cable connected therefore it is just the rods and the ground that are under test, not any cables.

Ze is a test from the MET in the cu testing the main earth cable and the rod as above so the reading will be a little bit higher due to resistance of the cable and the connections of the cable.

Zs is basically testing the resistance of the CPC at the furthest part of a circuit going via the met, onto the main earth cable to the rod.


Thats as i understand it and the most basic way I can put it to help anyone.
 
Just t answer the 2nd part of that...

If you install your rod, run the cable and then get a poor reading that is not acceptable you have to do it all again and re-position the rod. By doing an RA test you will find out if the location of the rod is acceptable or that another rod may be needed.
 
Thanks, Paul. Ze, of course, also includes the resistance/impedance of the supply line as well as the earth path.

As far as checking whether an earth rod is giving an acceptably low resistance to earth, nothing stops you doing a "Ze" test (providing the supply is available) before you run the earthing conductor (as it's resistance will generally be small compared to the RA of the rod).

But why does oldAL regard getting a RA figure as so important, when a Ze figure would seem to be the value that really matters at the end of the day?

Edit: According to page 39 of the BGB, RA includes the earthing conductor.
 
Last edited:
Edit: According to page 39 of the BGB, RA includes the earthing conductor.

GN3 2.7.12 Test method 1 and descriptions in the BGB of an RA conflict? Thats a surprise!

RA= resistance of the ground for an earth and a Ze = the combination of incoming nominal voltage to the resistance of earth via a rod.

Take a Ze on a TT system that is fine, done it loads of times but when you need to know the conditions of of the ground to give you a return earth path, you need to do an RA.
 