Plug in solar with a ring final?

Also needs permission from landlord
Won't happen in most cases. People will just buy them and plug them in, who cares about rules, instructions, safety, ...
Heck, tenants need permission from their landlord (and leaseholders also need permission from the freeholder or management company) to have Openretch come and throw fibre all over the front of the property - does that happen, does it **** (and contacting ORs multi dwelling unit was a waste of time as they just ignored me and did it anyway.)
and insurance
That will be a good one, who'll be liable if the tenant does something without permission, invalidates the insurance, and something happens ? I bet the tenant will just walk away and leave the landlord to sort out the ****.
 
BS1363-1
4 General
Plugs shall be so designed and constructed that in normal use their performance is reliable and minimizes the risk of danger to the user or to the surroundings. Such plugs shall be capable of meeting all the relevant requirements and tests specified in this part of BS 1363. Plugs shall not be used for the connection of electrical power generators to socket-outlets.
This will need rewriting, and it will need to include items to make it safe. Watching efixx around a year or more ago we see the problem with the test button on a RCBO with reverse current when test button is pressed.

As to if any problem, if test button not pressed I don't know, but when I tried to download a data sheet even when dated early this year, nothing on the sheet or the device to show if mono or bidirectional no load marked on the device or anything else to help.

So how can plug and play be authorised when we have no way to work out if the protection devices can work with it? Solar installers have to fit new equipment to be sure, this can't be done with Plug and Play, so can't see how it can be allowed?

As @Simon47 says, we will get people buying it anyway, so will we need to give sockets a code C2 if not protected by a RCD/RCBO which claims it is bidirectional? There is a potential danger if not bidirectional, so since we can't be sure plug and play solar will not be used, yes any non-bidirectional RCD/RCBO on socket circuits will get a code C2 on next EICR.
 
On another forum, they seem to think we should not need to protect people breaking the rules. A corner where a car doing 60 MPH may leave the road and go down a gorge does not need protection when in a 30 MPH area.
 
would it be that any bidirectional protection is built into the invertor part of the product? So it could be plug and play?

I cannot believe that wherever these products are already out on sale, and being used across Europe, that they don't have at least some safety rules to follow?
 
would it be that any bidirectional protection is built into the invertor part of the product? So it could be plug and play?
Yes, they will have to shut down if they lose their grid connection. That's even more necessary since not shutting down would mean a free plug could have it's pins live. Arguably, relying on that protection is questionable from a safety PoV (you don't generally rely on such electronic means as a safety function), but it appears that the powers that be aren't worried about that.

But back to the unidirectional RCD problem, it all depends on how fast the inverter shuts down. I suspect it might not be fast enough to prevent the sort of damage that's prompted this thread.
I cannot believe that wherever these products are already out on sale, and being used across Europe, that they don't have at least some safety rules to follow?
Having rules to follow, and actually following them aren't the same thing. Elsewhere I've read of people finding an isolated housing estate managing to continue running from the embedded solar for a while which means the anti-islanding protections have failed for at least some of the inverters.
I imagine our neighbours across La Manche have similar rules to us (or to what I assume we'll have at some point.)
 
Seems all now sorted UK Plug In Solar has confirmed.

The UK government has tightened its timeline for plug-in solar retail availability, confirming kits will be in shops "within a month" rather than the vaguer "within months" promised in March.
dated 2nd May 2026 so by end of this month is will be in the shops.

However, Is Plug-In Solar Legal in the UK? The Complete 2026 Guide reading this guide, there seems to be a problem with their English, as it says "Quick answer Yes, plug-in solar is legal in the UK since 24 March 2026." then it says you need/don't need an electrician, and suggests it should use a FCU which means it's not plugged in.

It is like saying you can ride a motorbike without a licence as long as it doesn't have a motor, in which case it's a bike not a motorbike.

It also says "UK Plug In Solar is an independent resource. We are not lawyers — this is informational, not legal advice." so what is the point of the website?
 
Seems all now sorted UK Plug In Solar has confirmed.

dated 2nd May 2026 so by end of this month is will be in the shops.

However, Is Plug-In Solar Legal in the UK? The Complete 2026 Guide reading this guide, there seems to be a problem with their English, as it says "Quick answer Yes, plug-in solar is legal in the UK since 24 March 2026." then it says you need/don't need an electrician, and suggests it should use a FCU which means it's not plugged in.

It is like saying you can ride a motorbike without a licence as long as it doesn't have a motor, in which case it's a bike not a motorbike.

It also says "UK Plug In Solar is an independent resource. We are not lawyers — this is informational, not legal advice." so what is the point of the website?
It says " Once the BSI standard publishes, you buy a certified kit, plug it into a 13A socket, and start generating. No electrician, no scaffolding, no planning permission."
 
If you have time to spare, this article may be of interest:

If you don't have time, here's a summary of what just might come from the BSI committee (which hasn't been formed yet):
Existing standards for inverters (IEC 62109 series) apply
Anti-Islanding behaviour (already covered by GS98) likely tightened.
Possible connector - Wieland GST18i3 as used in Germany for plug-in solar.
Timescale for publication of BSI Standard - late 2027


To quote a section of the article:

The standard will take time — but the direction is settled
Do not expect a published BSI standard before 2027. The announcement in March 2026 starts the process; it does not complete it. If you are waiting for a BSI-stamped product before buying, you will be waiting at least 18 months. The more practical approach is to buy a CE-marked product from a reputable manufacturer today, using the G98 notification pathway that already exists.

What This Means for Products You Can Buy Now​

The most common question from prospective buyers is: should I wait for BSI-standard products before buying? The answer, for most people, is no.

Products currently available from EcoFlow, Anker Solix, APsystems, Hoymiles, and other established brands carry CE marking, which means they have been assessed against relevant European electrical safety and electromagnetic compatibility standards. These products comply with the existing G98 requirements for anti-islanding. They are not unsafe or non-compliant; they simply predate the UK standard that is now being developed.

When the BSI standard is published, it is highly likely to be structured so that CE-marked products from established manufacturers either automatically comply or can be verified as compliant without hardware changes. The standard is being written by people who understand that the market already exists and cannot practically require millions of installed systems to be replaced.

🤔
 
I see @Avo Mk8 point, and also @Simon47 but forgetting about regulations for a moment, there is a clear problem insuring the units are only used in homes with bidirectional RCD/RCBO fitted.

Changing regulations will not change that.

Germany uses a non polarised plug, so has used double pole MCBs and RCBOs and I have not a clue if this means they are bidirectional.

But I have found data sheets saying a RCBO is bidirectional and duel switching, but there is no insignia to show which are which, so one can't write an instructions sheet to tell an ordinary person if it is safe or not.

Only way I can see it working is a massive list of part numbers showing which units are OK and which are not.
 
I see @Avo Mk8 point, and also @Simon47 but forgetting about regulations for a moment, there is a clear problem insuring the units are only used in homes with bidirectional RCD/RCBO fitted.

Changing regulations will not change that.
Absolutely. Bear in mind that most people just grab the thing out of the box and plug it in - the instructions only get opened if they can't get it to work. It really doesn't matter what warnings are used, they won't even be seen by most users.
Germany uses a non polarised plug, so has used double pole MCBs and RCBOs and I have not a clue if this means they are bidirectional.
2 pole and bi-directional are two separate features, having one does not imply having the other.
But I have found data sheets saying a RCBO is bidirectional and duel switching, but there is no insignia to show which are which, so one can't write an instructions sheet to tell an ordinary person if it is safe or not.
Indeed, it's usually on the side of the device, but generally not where a user can see it without opening up and partially dismantling dismantling the CU. And as I think we agree, most users won't know, won't care, and won't have seen any warnings in the manual they haven't opened.
 
To get paid for export one will need a G98/G99 completing, and it seems you need to submit these with V2G EV charging units, so technically you can as it stands use a standard EV charging socket for plug in solar, all legal.

However, most people when talking about a standard socket are not looking at V2G EV sockets but the BS 1363, we still have homes without RCD protection, and using old Wylex boards, which would actually not cause a problem with plug in solar, but how one can ensure sockets are suitable for solar I fail to see.

I look at UK 3 Pin Socket - Designed for Long Term EV Charging - BS 1363/EV and can't see any visible marking without removing it to show the socket is suitable. This
1781023562618.png
is on the back of the socket, but how will a user read that?
 
What akes you think only 5A flows ay the top [in your diagram] of the cricuit? It's a ring.
Yes there is some possibility of an overload, but not to the extent you show,
In any event at night or if the sun goes behind a cloud the 40A load on the two left twin sockets will trip the 32A MCB.
 
Well yesterday the consultation started. It closes 30th June, Open consultation Plug-in solar: Regulatory amendment and interim product specification some bits expected, 800 VA (watts) 3.5 amps, but no battery was not expected, a lot of the document talks about the instructions which should come with the array, the plug must be moulded not a clue why, and unless a modern consumer unit with RCBOs and labelled as to what feeds what, an electrician should be consulted, seems they incorrectly think type A RCBOs are bidirectional which is not correct.

The G98 is to be modified and will be required, it talks about meters able to record in 1/2 hour intervals. i.e. a Smart meter.
 
Well yesterday the consultation started. It closes 30th June, Open consultation Plug-in solar: Regulatory amendment and interim product specification some bits expected, 800 VA (watts) 3.5 amps, but no battery was not expected, a lot of the document talks about the instructions which should come with the array, the plug must be moulded not a clue why, and unless a modern consumer unit with RCBOs and labelled as to what feeds what, an electrician should be consulted, seems they incorrectly think type A RCBOs are bidirectional which is not correct.

The G98 is to be modified and will be required, it talks about meters able to record in 1/2 hour intervals. i.e. a Smart meter.
"Plug and play" suggests to the general public that they can go to shop, buy it, plug it in, and get going saving the planet... They will not read the instructions... they will not check they have an RCBO, whatever type... They will not care about any G98, or a Smart meter.

These handy online stores such as the South American river one, and the Chinese one that sells just about everything, will start to sell them with 13A plugs.... just a replugged european version..... and i'll bet they come with a higher capacity than 800W.

I guess we will just have to see what the powers that be tell us.... but personally, i think the more regulations they put in place, the more joe public will find ways to get around it.
 