Guest viewing is limited
Metal farm building currently has single phase TT supply with all the required bonding in place.
Client requires a 3 phase supply for a piece of equipment in this building - is it possible to bring a 3 phase supply from the farms house which is PME?
Sorry I should have said it's a storage building not used for livestock. Anybody got any ideas to a solution?
Doesn't matter. There is a high shock risk should you introduce a derived earth into a true earth (TT) environment. Why can't you TT it?
Sorry to bring this back up but I would like thoughts on my plan based on the above advise.
I'm going to bring 3phase PME supply across from main building to metal outbuilding but isolate the earth externally.
This means that I'll be TTing this new supply but what I need advise on is whether I sink a new Rod for this or would it be possible to use the Rod already installed for the current single phase TT supply the building uses (see original post for background info)
Thanks in advance
So long as the single phase supply is coming from the same supply transformer then you can use the existing earthing method. If the three phase supply and the single phase supply are from different transformers then you would be providing an earth link between supply transformers which could be a very bad idea. Circulating currents, and possibilities of transferring faults to other systems spring to mind.
If the supply cables are overhead follow them to see where they come from; if the single phase supply is from the same service head as the three phase supply they are the same;start with the basics and if there is no luck there then contact the DNO and hope.
You also need to consider the effects if there are two different supplies in the same building, but find out where they are fed from first.
Thanks in advance
its possible to use the existing electrode if you have confirmed that it is suitable for the job.
I'd probably look at augmenting it with additional new electrodes if possible to get the best earthing connection possible
You'll need to consider what to do about having the two different earthing systems in installation and so be no further forwards.
As both earthing systems would be TT is the risk not sufficiently reduced? (as apposed to a TT earth and PME earth)
If not it sounds like I either:
1.confirm both supplies are from same source and use one TT earthing system (possibly using multiple rods)
2.get rid of single phase supply and supply entire building from the new 3 phase PME supply (with TT earthing)
I'm onsite now having a look and it's a strange one to trace to be honest, the supply cable for the TT supply actually comes from underground with a PME sticker at the cutout but no earth block has been supplied - does this mean it has the potential to be a pme system however can't be because of the buildings use and therefore has been TT'd?
Thanks in advance
Can you not use the structural steel already in place as the electrode in the metal building?
Or isn't it imbedded in the ground?
It is permitted.
Without seeing it ... May be the original DNO supply required TT installation and at some point DNO did an upgrade and it became PME, but the installation has not been updated to use it as means of earthing (may require new bonding etc).
Newcastle upon Tyne
Pme TT in same farm building
Rkidcd,
Wilko,