Hi all, currently first fixing a new build, 2 bed bungalow. They are installing a 6kw air source heat pump. Electricity company is insisting on installing a polyphase supply. They have already run their cable from the pole to the property ready for connection, it has 3 cores. Can anyone tell me why they are insisting on two separate supplies. The property has a dual fuel cooker, 3 rings, 2 light circuits, smokes and an immersion.
 
possibly the 6kw pump is a motor that requires the 2 phases at alternate wavelength?
 
I really cannot see from what you describe why a 2/3 phase supply would be required.
A 6kW ASHP would not take much power, even the cooker is dual fuel and there is no electric shower.
The demand is going to be small compared to a large house so unless as said above the pump itself is 3 phase, which seems unlikely at that power there seems no cause.
Have they not said why they are insisting on this supply?
 
Yes 3 core and armour. It is a single phase pump. They are also insisting on a dual supply c/u. They say it is because of the demand of the pump. But as Richard says the demand is not that high.
 
They will be worried about the starting current of the motor. at 6kW if single phase this could be 183A (Direct On Line 7 x full load load). The kit may well have soft start but if you haven't told them they will assume DOL. Even with three phase the DOL starting current would be 61A.These starting currents can cause flicker on the supply and on neighbouring supplies which with frequent starting of a heat pump would be a problem. ALso, 183A may well take out a 100A fuse so you get into all sorts of other costs. Thats why they have gone three phase. The three cores are the phases and there will also be a concentric neutral earth (PEN) conductor. I'd be surprised if the heat pump is single phase - if it is you will need to ensure that it has soft start. Alt it may have multiple motors so you can wire as polyphase or arrange so they don't all start simultaneously.
 
Just as a quick check when you say 6kW ASHP I assume this is the heat output of the system and not the power of the pump itself, as I am assuming the 6kW is the system heating and the actual pump will be on something like a 16A breaker.
 
DNO Three core SWA?

Look again!

It will be a small 3C (possibly wave form) concentric to a 3Ph head.

Where do the two supplies come in to this?

You really need to go back to the Electrical Trainee training centre and start again.

Can’t wait for the how do I connect the AHP questions.
 
DNO Three core SWA?

Look again!

It will be a small 3C (possibly wave form) concentric to a 3Ph head.

Where do the two supplies come in to this?

You really need to go back to the Electrical Trainee training centre and start again.

Can’t wait for the how do I connect the AHP questions.

Tony,

With some of the ops questions I am having these thoughts , what do you think

Polyphase supply, cable already run from a pole, ASHP, 2 phase CU I am suspecting this is from our former colony of America or Canada
 