Evening all
went to a property today that had tripping RCD
found 2 32a rcd protected MCB's
with two cables in each
tested and found to be no continuity
on further investigation (3 hours) found the whole flat to be damp and low IR's everywhere
also chocky in the sockets where 3 2.5mm cables would not fit into socket
crimped cables that fell off when socket removed.
t and e going into the garden (which bizarrely was fine but left disconnected anyhow)
and 1 without an earth
the best was 5 x 2.5mm connected into 1 socket outlet.
we disconnected a total of 5 cables throughout the install and only lost 2 sockets
firstly this has me baffled but more importantly how do I impress to the landlord that this property which is also showing signs of water ingress at both left and right sides(semi basement property) is dangerous and actually needs something serious done
feel like I should issue him with a notice but am stumped to know how to approach it
 

Reply to possibly the worst one i have ever seen in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hey all, I'm looking for some advice to help me troubleshoot my strange issue with my consumer unit/fuse board on which my RCD keeps tripping...
Replies
25
Views
2K
Hi guys I have some industrial lighting circuits to wire in a workshop and was after some fresh ideas/suggestions as to how i could best do this...
Replies
12
Views
1K
We have had builders in, who have stopped for Xmas. My daughter tried to do a wash. The wash machine wouldnt. Its power socket is dead. I...
Replies
4
Views
652
I have a baffling problem with a newly-installed PIR floodlight and I'd like advice from the forum as to whether it's defective (and should be...
Replies
5
Views
533
  • Locked
  • Sticky
Beware a little long. I served an electrical apprenticeship a long time ago, then went back to full time education immediately moving away from...
Replies
55
Views
5K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock