revising for my 301 on Thursday and Ive come stuck on a question, any ideas?



A 30KW 3 phase delta connected motor has a power factor of 0.86 lagging. Calculate the line current.

answer is 50.35a but i dont know how to get there





thanks in advance :)
 
Last edited by a moderator:
rearrange the equation
power=volts*amps*SQ RT 3*power factor
to make amps the subject
30000=400*50.35*root3*0.86
 
Upvote 0
erm another quick problem.......


A medium sized factory has a three phase load of 50kVA and 30kVAr. Calculate the power factor?

a. 0.8



again im struggling with the formula, i must be arranging it in the wrong order, sorry to be a pain but anybody help us out?
 
Upvote 0
post the formulae, what is 30kvAr, should that read 30kvA, is 50kvA apparent power and 30kvA true power?
 
Last edited by a moderator:
Upvote 0
well it will be this wont it?

The power factor for a three-phase electric motor can be expressed as:
PF = P / [(3)1/2 U I] (2)
where
PF = power factor
P = power applied (W, watts)
U = voltage (V)
I = current (A, amps)
 
Upvote 0
sorry i must be using the wrong forumula then, this is exactly how the question reads:


A medium sized factory has a three phase load of 50 kVA and 30 kVAr. Calculate the power factor
 
Upvote 0
to me, and im pretty sure im right(99.9%), you have a factory with apparent power 50kvA and true power of 30kvA, power factor=true power/apparent power, 30kvA/50kvA=0.6 which means your answer is wrong. text books with incorrect answers are not uncommon. does this sound plausible?? also i'm not sure what kvAr is?
 
Upvote 0
to me, and im pretty sure im right(99.9%), you have a factory with apparent power 50kvA and true power of 30kvA, power factor=true power/apparent power, 30kvA/50kvA=0.6 which means your answer is wrong. text books with incorrect answers are not uncommon. does this sound plausible?? also i'm not sure what kvAr is?

kvar is Reactive Power so i think the question is right im just not getting it. :confused:

or you could be right and the paper is wrong lol
 
Upvote 0
you are right, i didnt think you would that at level 3, i cant cope with these questions after a few beers so ill get back to you tomorrow nite if thats ok
 
Upvote 0
Best EV Chargers by Electrical2Go! The official electric vehicle charger supplier.

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
Power factor question
Prefix
N/A
Forum
Electrician Courses : Electrical Quals
Start date
Last reply date
Replies
29
Unsolved
--

Advert

Thread statistics

Created
DT1878,
Last reply from
DT1878,
Replies
29
Views
4,453

Advert

Electrical Courses

This is the main Electrical Courses at ElectriciansForums.net. Find local recommended electricians courses. Avoid training "company" scams. Always go view the training centre before booking any electrical courses.
Back
Top