Question 2:

Which person makes the recommendation for the interval to the first periodic inspection and testing of an electrical installation?

(Provide Reg No)

A) The person ordering the work.
B) The designer
C) The installer
D) The person carrying out the initial verification.
 
Question 3:

The maximum earth fault loop impedance for 5s disconnection time with Uo of 230v for a 160A fuse to BS 88-2 is which of the following:

(Including Reg No)

A) 0.19 ohms
B) 0.27 ohms
C) 0.33 ohms
D) 0.70 ohms
 
Question 3:

The maximum earth fault loop impedance for 5s disconnection time with Uo of 230v for a 160A fuse to BS 88-2 is which of the following:

(Including Reg No)

A) 0.19 ohms
B) 0.27 ohms
C) 0.33 ohms
D) 0.70 ohms
i got that one, but would need to look up the previous ones. surprising what you forget when dementia and/or beer. kicks in,:D:D:D.
 
Quite interesting. I suppose the other two are not often used.

Good practice for us all these questions.
pm'd you.
 
Question 4:

Using Table 54.7 of BS 7671, what is the minimum cross-sectional area of a protective conductor to be used with a 70mm line conductor?

A) 16mm
B) 25mm
C) 35mm
D) 50mm
 