Question 3:
The maximum earth fault loop impedance for 5s disconnection time with Uo of 230v for a 160A fuse to BS 88-2 is which of the following:
(Including Reg No)
A) 0.19 ohms
B) 0.27 ohms
C) 0.33 ohms
D) 0.70 ohms
B) 0.27 ohms
Table 41.4 page 63
Question 3:
The maximum earth fault loop impedance for 5s disconnection time with Uo of 230v for a 160A fuse to BS 88-2 is which of the following:
(Including Reg No)
A) 0.19 ohms
B) 0.27 ohms
C) 0.33 ohms
D) 0.70 ohms
Question 4:
Using Table 54.7 of BS 7671, what is the minimum cross-sectional area of a protective conductor to be used with a 70mm line conductor?
A) 16mm
B) 25mm
C) 35mm
D) 50mm
I used the wrong table.B) 25 mm table 54.8 (18th edition) page 203