B

Buzz1980

Hi all

regarding prescribed wiring zones. Are these wiring zones only relevant to domestic installs ? Or even installs that are supervised, such as a hotel or restaurant? Thanks in advance
 
Anywhere that cables are buried in a wall at less 50mm deep. Unless one of the other conditions is met, for example, earthed metal conduit.
 
Hi thanks for the reply. Yeah so doesn’t matter if domestic or commercial or there is instructed person. Does RCD protection not give this enough protection or still requiring earth metallic wiring system to meet regs ?
 
30mA RCD will comply with 522.6, but cables must be installed in prescribed zones. otherwise some might think that a builder had done it.
 
So if cables are out with prescribed zones then installing on 30ma RCD with then meet regs ? So is the earth metallic conduit only required for if not installed on RCD ?
 
the whole purpose is to eliminate danger from a nail or screw penetrating the cable. earthed metal conduit would cause a L -E short, tripping the OCPD. a RCD would trip on the leakage > 30mA. either way, the supply wouldbe isolated, preventing danger.
 
Ok thanks for the replies. So basically installers can run cables where they want then as long as it’s on a 30ma RCD. Not the best practise but if it complies then can’t really say anything if cables not in prescribed zones then.
 
Ok thanks for the replies. So basically installers can run cables where they want then as long as it’s on a 30ma RCD. Not the best practise but if it complies then can’t really say anything if cables not in prescribed zones then.
This is not correct.

A careful reading of 522.6.202 through to 522.6.204, including all the notes, shows that cables installed in walls at a depth of less than 50mm shall be installed in safe zones AND be additionally protected by 30mA RCDs.

Alternatively, we can install cables outside of the zones only if suitably protected mechanically, or form part of a SELV or PELV circuit.
 