G
Geoffsd
Those are the recommended OPDs to use for different showers not the amperage of the units.its a triton shower, 2 sizes, it states 9.8k - 45A & 8.5k - 40A. Its currently being protected by a 40A bs1361 cartridge fuse, again another reason why i pondered the voltage in the calc
The MIs should be followed.
I'm not talking about two sizes but two voltages.
You cannot quote a wattage without stating the voltage.
My previous post is correct for a shower quoted by the manufacturer as 9.8kW @ 240V.