its a triton shower, 2 sizes, it states 9.8k - 45A & 8.5k - 40A. Its currently being protected by a 40A bs1361 cartridge fuse, again another reason why i pondered the voltage in the calc
Those are the recommended OPDs to use for different showers not the amperage of the units.
The MIs should be followed.

I'm not talking about two sizes but two voltages.
You cannot quote a wattage without stating the voltage.

My previous post is correct for a shower quoted by the manufacturer as 9.8kW @ 240V.
 