Hello all,

A quick question... when selecting a protective device should you use the nominal voltage or the measured voltage?

example
9.8k / Uo = 42.6A select 50A mcb
9.8 / measured voltage 245V = 40A select 40A mcb

Thanks in advance
 
I'm assuming that what you're talking about is protecting a shower. In which case, the 9.8kW will be specified at a particular supply voltage. If you increase the supply voltage you will INCREASE the current and the power, so you calculation is incorrect. What's fixed is the heater resistance (or nearly so), not the power.

Generally best just to use the nominal figures.
 
For you,re 9.8KW @ 230V the resistance would be 5.4Ώ

So for you're 245V supply it works out at 45.5A assuming a linier coefficient of resistance/temperature. Which you can't.
 
Handysparks, Yes its a shower. 10mm cable. Manufacturers instruction say 45A breaker except cant get wylex 45A that easily. Shall i go with 50A breaker then?

Tony, what is "linier coefficient of resistance/temperature" can you explain further please?
 
Unless things have drastically changed in design, you are suppose to design everything at Uo

Most showers though are rated still at 240v which does make our life a little complicated but if you design to 230v then you are erring on the side of caution by saying that your load is going to be higher.

You never though design to RMS .....................
 
I would stick it on a 50a

Tony, what is "linier coefficient of resistance/temperature" can you explain further please?

No idea and I don't even know what Linear coefficient of resistance/temperature is either, don't think it's relevant
 
Linear coefficient is really to do with thermal expansion and no on a domestic shower circuit I don't think there is a lot to worry about ..............Think our Tony was slightly pulling the leg
 
Handysparks, Yes its a shower. 10mm cable. Manufacturers instruction say 45A breaker except cant get wylex 45A that easily. Shall i go with 50A breaker then?

Tony, what is "linier coefficient of resistance/temperature" can you explain further please?

If you're using 10mm² T&E then, providing your correction factors don't drag the current carrying capacity down too far, a 50A breaker will be fine.

I think Tony meant to say that, if the resistance of the heater remains constant with current/power, then the current will be... This is probably reasonable, as the element is surrounded by water, so it's temperature, and therefore resistance, isn't going to vary much with current. Unlike a filament lamp, where the resistance changes hugely with current and filament temperature.
 
yes, the current carrying cap was on my mind. its partly clipped direct, then along the floor void and up through the stud to the 45A switch on the landing wall not much to derate the cable. oh, now is that a problem 45A rated switch/50A breaker?
thanks
 
yes, the current carrying cap was on my mind. its partly clipped direct, then along the floor void and up through the stud to the 45A switch on the landing wall not much to derate the cable. oh, now is that a problem 45A rated switch/50A breaker?
thanks

No..................
 
9.8k / Uo = 42.6A select 50A mcb
9.8 / measured voltage 245V = 40A select 40A mcb
Does the manufacturer quote 9.8kW @ 240V ?

If so, then that is equivalent to 8.99kW @ 230V.

8990 / 230 = 39.1A - these are the figures that should be used in calculations
 
its a triton shower, 2 sizes, it states 9.8k - 45A & 8.5k - 40A. Its currently being protected by a 40A bs1361 cartridge fuse, again another reason why i pondered the voltage in the calc
 
its a triton shower, 2 sizes, it states 9.8k - 45A & 8.5k - 40A. Its currently being protected by a 40A bs1361 cartridge fuse, again another reason why i pondered the voltage in the calc
Those are the recommended OPDs to use for different showers not the amperage of the units.
The MIs should be followed.

I'm not talking about two sizes but two voltages.
You cannot quote a wattage without stating the voltage.

My previous post is correct for a shower quoted by the manufacturer as 9.8kW @ 240V.
 

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
protective device selection
Prefix
Forum
UK Electrical Forum
Start date
Last reply date
Replies
15

Advert

Thread statistics

Created
Sbc,
Last reply from
Geoffsd,
Replies
15
Views
2,474

Advert