Difficult to know what to install these days they all have problems , square D to expensive and crap curly leads , MK poor quality , Wylex again poor quality and customer service diabolical , think ill make my own up , 99.999 % of boards are made in china even the british ones
 
Wouldn't waste my time looking around - proteus really is cheap & nasty stuff - has one of their CUs at home when I moved in - didn't stay installed there for long. Changed first chance I got.
 
Difficult to know what to install these days they all have problems , square D to expensive and crap curly leads , MK poor quality , Wylex again poor quality and customer service diabolical , think ill make my own up , 99.999 % of boards are made in china even the british ones

I have just had issues with 8 , 4 way 3ph ABB boards fitted with 250 amp main switches that had only been in service less than a week . Some of the burnt out boards are back with ABB being inspected at the moment !?
 
I must admit when I open up a CU I tend to go around the connections and find a few that are slack why because the majority of my work is fault finding repairs. So for me this is down to the person putting the gear in
 
I must admit when I open up a CU I tend to go around the connections and find a few that are slack why because the majority of my work is fault finding repairs. So for me this is down to the person putting the gear in

Same as , but after the first one burnt out we went around and checked all connections again ! This was after already double checking them before commissioning them in the first place . ( With a torques driver )
 
Same as , but after the first one burnt out we went around and checked all connections again ! This was after already double checking them before commissioning them in the first place . ( With a torques driver )

For me I think this is the bulk of CU probl would be 90% bad or poor connections and 10% faulty equipment ie mcb . I had a job on Friday with a faulty Hager mcb I replaced it then went around the the rest of the connection
 
I have only ever had one other faulty mcb burn out , and that was on a shockingly ****e "Basics" board that one of the wholesalers gave to me to try out . Luckily I had passed it on free of charge to the customer , but even then it still looked bad so we ended up swapping the board free of charge again for a Hagar one !
 
I must admit when I open up a CU I tend to go around the connections and find a few that are slack why because the majority of my work is fault finding repairs. So for me this is down to the person putting the gear in
and time & again i`v said in here to `rattle/manipulate` stranded cables whilst tightening in order to bed the strands down nicely...

and a torque driver alone wont cut it i`m afraid....
its about technique...
 
I agree Glen , and to be honest find the torque driver a bit of an insult in some respects ! But after being terminated by one of our site foremen and then double checked by the same chap before commissioning , I then sent another man to check again after the first incident then a different man after the next incident and then I went in after the third incident and ****'ed off the torque driver and pinched them up to what I thought acceptable ! And so far , touch wood !!! So considering four different blokes have now either made off originally or checked the terminations 5 times now ( one of them being an ex HV installer ! ), I am minded to think it is not operator error on this one . But I have a feeling the report that comes back will suggest so anyway !
 
I agree Glen , and to be honest find the torque driver a bit of an insult in some respects ! But after being terminated by one of our site foremen and then double checked by the same chap before commissioning , I then sent another man to check again after the first incident then a different man after the next incident and then I went in after the third incident and ****'ed off the torque driver and pinched them up to what I thought acceptable ! And so far , touch wood !!! So considering four different blokes have now either made off originally or checked the terminations 5 times now ( one of them being an ex HV installer ! ), I am minded to think it is not operator error on this one . But I have a feeling the report that comes back will suggest so anyway !
torque drivers are a stupid fad...
all this will blow over....
in the meantime you can carry on `feeling` when its there...
tried n trusted....
 
torque drivers are a stupid fad...
all this will blow over....
in the meantime you can carry on `feeling` when its there...
tried n trusted....

Damn stuff nearly killed me, I found out to my cost that it is quite easy to cross phase 3-phase circuit breakers and shorting the lot out, made me jump a bit as well
 