Lenny

-
Reaction score
14
Hi all.

Could someone please confirm where to connect a 4-20mA pressure transducer to AI2 in the attached photo. I believe it’s terminals 7 & 8 but the pump is not responding at all.

Thanks.

ADB920EC-18CB-451A-8FF1-E78CD71E3F43.jpeg
 
Basically you have a circulation pump with an attached inverter?

The analog inputs are AI1 and AI2 you can use either, you’ll have to configure the inverter parameters to allow PID control as per page 17 onwards of the manual, have you done this? Depends on what your trying to do with it though.
 
Last edited:
Thanks for the reply.

AI2 has been configured in the grundfos go app for pump control via discharge pressure into a private water main. I've taken a 24V supply to the transducer from terminal 8 with the return from the transducer into terminal 7.

Screen is connected to gnd. The pump doesn't control to the pressure setrpoint at all.
 
Is there a jumper between 2 and 6 for start signal?
 
Yes.

Starting to think it may be an issue with airlocking around the transducer due to its position as part of the pump assembly. With the loop calibrator connected in place of the transducer, the pump responds as it should.
 
If the polarity is correct and the transmitter is healthy then I would say that’s the only thing it could be unless it has the wrong range of course.
 
Last edited:
Sorry for not following up.

Turns out the fault was due to airlocking around the PT. The new VSD didn't like the setup so I moved the PT further along the discharge pipework and it worked fine.

Thanks for the replies, nothing worse than when you start doubting yourself!!
 

Reply to PT Connection To Pump in the Industrial Electricians' Talk area at ElectriciansForums.net

Similar Threads

Good evening all, I’m currently part way through my apprenticeship and we are working on IB, IN, IZ and IT and volt drop today. And it got me...
Replies
4
Views
436
I've pretty much sussed out the wiring for the radiators and underfloor heating, thanks to help from the forum. I do have one more question...
Replies
6
Views
668
Hi all, Thank you in advance... So I had an electrician put in some FCUs on spurs to a couple of outside lights.. this one was in readiness to...
Replies
17
Views
625
I recently purchased a rural property in Arizona. The property receives power from APS, the local electric utility. Power arrives from the...
Replies
3
Views
868
Hi All, I own a country Villa out in the Spain countryside. Was having problems with water pressure so local tradesmen advised to get a water...
Replies
14
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock