As per previous thread a wile back the pub build is now under way and upto roof level,just wanted to check my proposed electrical feed if I can please?
Earthing is TN-S not TNCS previously thought,(customer has now cleared the meter cupboard!)

Anyway loading in the pub is as follows
1 x 32a rfc 12 points
1 x 6a lighting
1 x 16a radial for ufh at 3kw (fused at sfcu)
1 x 16 a radial for water heater (no spec yet but assuming greater than 2kw)

Other loading not yet determined is a macerated toilet but hoping to spur from rfc

No extraneous parts, water and waste all in plastic
Proposed set up
Split tails into Henley and into small 2 way Cu with 100a main switch and 63a mcb, 10mm 3 core swa upto pub into sub db main switch and all circuits rcbo to relevant sizing
Have I missed anything?
As always all responses much appreciated
 

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

Baddegg

Esteemed
Arms
Supporter
Patron
-
Joined
Location
Southsea
If you're a qualified, trainee, or retired electrician - Which country is it that your work will be / is / was aimed at?
United Kingdom
What type of forum member are you?
Practising Electrician (Qualified - Domestic or Commercial etc)
If other, please explain
?

Thread Information

Title
Pub project now under way............
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
18
Unsolved
--

Advert

Thread statistics

Created
Baddegg,
Last reply from
Squid,
Replies
18
Views
1,780

Advert

Back
Top